Re: [time-nuts] Line Voltage [Was: Anyone (ideally in the UK) ...]

PK
Poul-Henning Kamp
Mon, Jan 2, 2017 6:14 PM

What modern loads are actually sensitive to high (say, +10 to +20%) line
voltage?

In EU you're supposed to have 230V +/- 6% in your outlet.

The way this was arrived at was:

A lot of europe used 220V +/- 10% = [198..242] V

Brittain used 240V +/- 10% = [216..264] V

Take the average of the two, and use the low max and high min as limits

QED:  230V +/- 6% = [216..244]

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

-------- In message <CAJ_qRvb6-79y99aFgAUowZjJcEUK4LWeAEHwDgRqNOsGQVzneQ@mail.gmail.com> , Tim Shoppa writes: >What modern loads are actually sensitive to high (say, +10 to +20%) line >voltage? In EU you're supposed to have 230V +/- 6% in your outlet. The way this was arrived at was: A lot of europe used 220V +/- 10% = [198..242] V Brittain used 240V +/- 10% = [216..264] V Take the average of the two, and use the low max and high min as limits QED: 230V +/- 6% = [216..244] -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence.
LM
LEE MUSHEL
Mon, Jan 2, 2017 9:37 PM

Another one of those fascinating "threads!"  I have lived through the claimed 110, 117 and 120 volt periods and have been apparently lucky enough to not have suffered any device damage.  At present I live on a hill and do worry about lightning strikes to ham radio antennas.  The last time I counted I had over 20 standard eight foot plated ground rods driven at various places and the entrance point of these antennas to the house is protected by an additional 6 rods.  All wiring in the house is either thin wall tubing or other armored cable.  Thus I effectively have building perimeter protection as well.  All grounds are tied together along with the power neutral.  I also have an automatic transfer backup alternator with separate ground also tied to the entire system.  I do disconnect antennas during storm threats but in the past thirty years have yet to have any "over voltage" damage.  From time to time I do check the line voltage but not with any NBS standard voltmeter and have found that it does "drift" between 120 and 126  which I feel is outstanding given the general circumstances which include being several miles from the distribution point along a rural road and the possibility of some fairly demanding motor starting loads that I deal with.  My input panel is over 200 ft. from the farmer's electric co-op transformer which I used to share with two neighbors but now I have "my own."  Yes, I do have lightning rod protection.

73

Lee  K9WRU
----- Original Message -----
From: Poul-Henning Kamp phk@phk.freebsd.dk
To: Discussion of precise time and frequency measurement time-nuts@febo.com, Chuck Harris cfharris@erols.com
Sent: Mon, 02 Jan 2017 12:55:58 -0500 (EST)
Subject: Re: [time-nuts] Line Voltage - USA


In message 586A8B40.4050806@erols.com, Chuck Harris writes:

Back in the dark ages of ~220V electrical distribution systems in
Europe, the reaping due to unintentional grounding of a ~220V wire
was  so common and extreme, whole house ground fault interrupters
were mandated for all residential/small business power systems
therein.

Close, but no cigar.

The main problem was that in many countries outlets did not have a
protective ground terminal.

That meant that an internal fault in your appliance had a 50/50
chance of lighting up some exterior metal part you could touch.

The "obvious solution" isn't obvious in countries where the geography
does not allow you to obtain proper "protective ground".  Norway being a
good example.

But even countries with the "obvious solution" of protective ground
in all outlets saw problems, because it took 10-16 ampere misdirected
current to blow the fuse, and you can light most flameable stuff
with a lot less energy than that.

The "Residual Current Device" solved both problems.

RCD's even protect you from internal faults where proper protective
ground is not available, by providing neutral from "outside" the
RCD as PG in the installation.  You'll still be (horribly!) exposed
of an accident in the distribution grid (or lightning!) fires up
the neutral, but that's simply life - or death - without a grounding
rod.

--
Poul-Henning Kamp      | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG        | TCP/IP since RFC 956
FreeBSD committer      | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Another one of those fascinating "threads!" I have lived through the claimed 110, 117 and 120 volt periods and have been apparently lucky enough to not have suffered any device damage. At present I live on a hill and do worry about lightning strikes to ham radio antennas. The last time I counted I had over 20 standard eight foot plated ground rods driven at various places and the entrance point of these antennas to the house is protected by an additional 6 rods. All wiring in the house is either thin wall tubing or other armored cable. Thus I effectively have building perimeter protection as well. All grounds are tied together along with the power neutral. I also have an automatic transfer backup alternator with separate ground also tied to the entire system. I do disconnect antennas during storm threats but in the past thirty years have yet to have any "over voltage" damage. From time to time I do check the line voltage but not with any NBS standard voltmeter and have found that it does "drift" between 120 and 126 which I feel is outstanding given the general circumstances which include being several miles from the distribution point along a rural road and the possibility of some fairly demanding motor starting loads that I deal with. My input panel is over 200 ft. from the farmer's electric co-op transformer which I used to share with two neighbors but now I have "my own." Yes, I do have lightning rod protection. 73 Lee K9WRU ----- Original Message ----- From: Poul-Henning Kamp <phk@phk.freebsd.dk> To: Discussion of precise time and frequency measurement <time-nuts@febo.com>, Chuck Harris <cfharris@erols.com> Sent: Mon, 02 Jan 2017 12:55:58 -0500 (EST) Subject: Re: [time-nuts] Line Voltage - USA -------- In message <586A8B40.4050806@erols.com>, Chuck Harris writes: >Back in the dark ages of ~220V electrical distribution systems in >Europe, the reaping due to unintentional grounding of a ~220V wire >was so common and extreme, whole house ground fault interrupters >were mandated for all residential/small business power systems >therein. Close, but no cigar. The main problem was that in many countries outlets did not have a protective ground terminal. That meant that an internal fault in your appliance had a 50/50 chance of lighting up some exterior metal part you could touch. The "obvious solution" isn't obvious in countries where the geography does not allow you to obtain proper "protective ground". Norway being a good example. But even countries with the "obvious solution" of protective ground in all outlets saw problems, because it took 10-16 ampere misdirected current to blow the fuse, and you can light most flameable stuff with a lot less energy than that. The "Residual Current Device" solved both problems. RCD's even protect you from internal faults where proper protective ground is not available, by providing neutral from "outside" the RCD as PG in the installation. You'll still be (horribly!) exposed of an accident in the distribution grid (or lightning!) fires up the neutral, but that's simply life - or death - without a grounding rod. -- Poul-Henning Kamp | UNIX since Zilog Zeus 3.20 phk@FreeBSD.ORG | TCP/IP since RFC 956 FreeBSD committer | BSD since 4.3-tahoe Never attribute to malice what can adequately be explained by incompetence. _______________________________________________ time-nuts mailing list -- time-nuts@febo.com To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.
V
Vlad
Tue, Jan 3, 2017 4:05 PM

Speaking about MAIN... I was interesting to see if "leap second" event
has correlation with MAIN frequency fluctuation

Here is graphs for the MAIN periods recorded. Note: The data on the
charts is "smoothed" by Bezier curves

I could see some "surge" which starts to climb in December 30 and end at
Dec 31 at the time close to the "leap second" event. But not sharp.

For 16-12-29 00:00 to 17-01-02 00:00
http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png

For Dec 31:
http://www.patoka.ca/OCXO/60hz-periods-Dec31.png

It will be interesting to see/compare if anybody else has similar stats.

Regards,
Vlad

On 2017-01-02 13:00, Tim Shoppa wrote:

What modern loads are actually sensitive to high (say, +10 to +20%)
line
voltage?

Old incandescent light bulbs were among the most sensitive loads in the
past (so much so, that 130V light bulbs were commonly available from
the
industrial suppliers).

I would naively expect the modern CFL's and LED replacements to be fine
with higher line voltage because they have their own built-in switching
regulation.

A lot of modern electronic equipment with switching supplies, are just
fine
at +20% line voltage and may even run cooler.

Tim N3QE

On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom time@radio.sent.com
wrote:

There are a couple of recent threads concerning the power line mains
voltage standards. After a bit of research and thinking, I have found
that this is a complex topic. The simple answer is:

  • The standard in the US for the past 50 years has been 120/240 V +/-
    5%
    RMS at the service entrance to the building. This is a range of
    114/228 V to 126/252 V.
  • The load voltage could be as low as 110/220 V and as high as 125/250
    V
    and be within specifications.

There are two voltage measurement points to consider:

(1) Service voltage: This is the RMS voltage measured at the service
entrance to the building (at the metering point).
(2) Utilization voltage: This is the RMS voltage measured at the load.
It might be measured at an unused socket in a power strip feeding
several pieces of electronic equipment, for example. There are of
course many different utilization voltages present in a home or
business, depending on where you make the measurement.

Most US homes and small businesses are powered by what is commonly
called a "split-phase" 240 V feed. The final distribution system
transformer has a 240 V center-tapped secondary. The center tap is
grounded, and three wires are fed to the building (actually it might
be
up to around 6 houses):
(1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to
the
neutral or 240 V to Leg L2.
(2) Neutral (white wire) -- This wire is grounded at the distribution
system and at the service entrance to the building.
(3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L1.

Large appliances and HVAC systems are usually connected across L1-L2
(240 V), while most sockets are on circuits either connected across
L1-
neutral (120 V) or L2-neutral (120 V).

The voltages I have described are the current standardized values for
the service voltage which have been in general use for about 50 years
(120/240 V +/- 5%). I believe that the original systems installed
before
1940 were designed for a 110/220 V nominal service voltage, but after
a
report in 1949 the nominal service voltage was increased to 117/234 V,
as specified in ANSI C84.1-1954. After research in actual buildings,
in
the 1960's the nominal service voltage was increased again, to 120/240
V
in the ANSI C84.1-1970 standard. The purpose is to keep the
utilization
voltage at the load above 110/220 V.

The voltage at the service entrance should in most cases be in Range A
(120/240V +/-5%). On each 120V leg the service voltage should
therefore
be between 114 and 126 V. The utilization voltage at the load should
be
between 110 and 125 V due to losses in building wiring.

See details of the current specifications at:

http://www.pge.com/includes/docs/pdfs/mybusiness/
customerservice/energystatus/powerquality/voltage_tolerance.pdf

These voltage specifications were designed for resistive loads and
measurement of the true RMS voltage. In most electronic equipment
built
over the past 50 years, the power supply input circuitry is basically
a
rectifier connected to a smoothing capacitor. This leads to high input
current surges during the peaks of the waveform, so that the peak
voltage is reduced much more by the building wiring resistance than if
the load was resistive for the same power consumption.

So the waveform shape at different utilization locations in a building
(with active equipment loads) may be different, so the voltage
measured
by different AC measuring instruments can differ. Many meters are full
wave average measuring but calibrated so they only read RMS voltage
correctly on pure sinewaves. Other meters are true RMS measuring and
will read very close the correct RMS voltage even if the waveform is
distorted.

Bill Byrom N5BB

On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote:

Mark,

CSA have standards for over and under voltage, Typical no more that 3%
over and 5% under if memory serves me.

This might help (

fia3660-voltagedropcalc.pdf

)

The power companies here in Alberta are generally good about fixing

problems with line regulation.

There can be problems with industrial areas and big welders or motors
staring as I am sure you know.

I am sure they do not want the bill for replacing equipment that was

subjected to over voltage.

On UPSs: I am sure you are aware that may of them are not TRUE
sine wave
so the DMM may not read correctly.

Mitch


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
WBW,

V.P.

Speaking about MAIN... I was interesting to see if "leap second" event has correlation with MAIN frequency fluctuation Here is graphs for the MAIN periods recorded. Note: The data on the charts is "smoothed" by Bezier curves I could see some "surge" which starts to climb in December 30 and end at Dec 31 at the time close to the "leap second" event. But not sharp. For 16-12-29 00:00 to 17-01-02 00:00 http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png For Dec 31: http://www.patoka.ca/OCXO/60hz-periods-Dec31.png It will be interesting to see/compare if anybody else has similar stats. Regards, Vlad On 2017-01-02 13:00, Tim Shoppa wrote: > What modern loads are actually sensitive to high (say, +10 to +20%) > line > voltage? > > Old incandescent light bulbs were among the most sensitive loads in the > past (so much so, that 130V light bulbs were commonly available from > the > industrial suppliers). > > I would naively expect the modern CFL's and LED replacements to be fine > with higher line voltage because they have their own built-in switching > regulation. > > A lot of modern electronic equipment with switching supplies, are just > fine > at +20% line voltage and may even run cooler. > > Tim N3QE > > On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom <time@radio.sent.com> > wrote: > >> There are a couple of recent threads concerning the power line mains >> voltage standards. After a bit of research and thinking, I have found >> that this is a complex topic. The simple answer is: >> >> >> * The standard in the US for the past 50 years has been 120/240 V +/- >> 5% >> RMS at the service entrance to the building. This is a range of >> 114/228 V to 126/252 V. >> * The load voltage could be as low as 110/220 V and as high as 125/250 >> V >> and be within specifications. >> >> >> There are two voltage measurement points to consider: >> >> (1) Service voltage: This is the RMS voltage measured at the service >> entrance to the building (at the metering point). >> (2) Utilization voltage: This is the RMS voltage measured at the load. >> It might be measured at an unused socket in a power strip feeding >> several pieces of electronic equipment, for example. There are of >> course many different utilization voltages present in a home or >> business, depending on where you make the measurement. >> >> >> Most US homes and small businesses are powered by what is commonly >> called a "split-phase" 240 V feed. The final distribution system >> transformer has a 240 V center-tapped secondary. The center tap is >> grounded, and three wires are fed to the building (actually it might >> be >> up to around 6 houses): >> (1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to >> the >> neutral or 240 V to Leg L2. >> (2) Neutral (white wire) -- This wire is grounded at the distribution >> system and at the service entrance to the building. >> (3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the >> neutral or 240 V to Leg L1. >> >> >> Large appliances and HVAC systems are usually connected across L1-L2 >> (240 V), while most sockets are on circuits either connected across >> L1- >> neutral (120 V) or L2-neutral (120 V). >> >> >> The voltages I have described are the current standardized values for >> the service voltage which have been in general use for about 50 years >> (120/240 V +/- 5%). I believe that the original systems installed >> before >> 1940 were designed for a 110/220 V nominal service voltage, but after >> a >> report in 1949 the nominal service voltage was increased to 117/234 V, >> as specified in ANSI C84.1-1954. After research in actual buildings, >> in >> the 1960's the nominal service voltage was increased again, to 120/240 >> V >> in the ANSI C84.1-1970 standard. The purpose is to keep the >> utilization >> voltage at the load above 110/220 V. >> >> >> The voltage at the service entrance should in most cases be in Range A >> (120/240V +/-5%). On each 120V leg the service voltage should >> therefore >> be between 114 and 126 V. The utilization voltage at the load should >> be >> between 110 and 125 V due to losses in building wiring. >> >> >> See details of the current specifications at: >> >> http://www.pge.com/includes/docs/pdfs/mybusiness/ >> customerservice/energystatus/powerquality/voltage_tolerance.pdf >> >> >> These voltage specifications were designed for resistive loads and >> measurement of the true RMS voltage. In most electronic equipment >> built >> over the past 50 years, the power supply input circuitry is basically >> a >> rectifier connected to a smoothing capacitor. This leads to high input >> current surges during the peaks of the waveform, so that the peak >> voltage is reduced much more by the building wiring resistance than if >> the load was resistive for the same power consumption. >> >> >> So the waveform shape at different utilization locations in a building >> (with active equipment loads) may be different, so the voltage >> measured >> by different AC measuring instruments can differ. Many meters are full >> wave average measuring but calibrated so they only read RMS voltage >> correctly on pure sinewaves. Other meters are true RMS measuring and >> will read very close the correct RMS voltage even if the waveform is >> distorted. >> -- >> >> Bill Byrom N5BB >> >> >> >> >> >> On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote: >> >> > Mark, >> >> > >> >> > CSA have standards for over and under voltage, Typical no more that 3% >> > over and 5% under if memory serves me. >> >> > >> >> > This might help ( >> >> > http://www.safetyauthority.ca/sites/default/files/csa- >> fia3660-voltagedropcalc.pdf >> > ) >> >> > The power companies here in Alberta are generally good about fixing >> >> > problems with line regulation. >> >> > There can be problems with industrial areas and big welders or motors >> > staring as I am sure you know. >> >> > I am sure they do not want the bill for replacing equipment that was >> >> > subjected to over voltage. >> >> > >> >> > On UPSs: I am sure you are aware that may of them are not TRUE >> > sine wave >> > so the DMM may not read correctly. >> >> > >> >> > Mitch >> >> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/ >> mailman/listinfo/time-nuts >> and follow the instructions there. >> > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to > https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there. -- WBW, V.P.
DD
Dr. David Kirkby (Kirkby Microwave Ltd)
Tue, Jan 3, 2017 4:17 PM

On 2 January 2017 at 18:14, Poul-Henning Kamp phk@phk.freebsd.dk wrote:


In message <CAJ_qRvb6-79y99aFgAUowZjJcEUK4LWeAEHwDgR
qNOsGQVzneQ@mail.gmail.com>
, Tim Shoppa writes:

What modern loads are actually sensitive to high (say, +10 to +20%) line
voltage?

In EU you're supposed to have 230V +/- 6% in your outlet.

The way this was arrived at was:

A lot of europe used 220V +/- 10% = [198..242] V

Brittain used 240V +/- 10% = [216..264] V

Take the average of the two, and use the low max and high min as limits

QED:  230V +/- 6% = [216..244]

Do you have a reference to this +6%? I've heard from various sources that
the UK is 230 -6%/+10%.  If the EU dictates otherwise, then I'm certainly
over the 6% limit. I may or may not be over the 10% limit.

While the UK is still in the EU, it would be good to get this resolved,
since we will be leaving in just over 2 years.

Rules in Brussels override those made in the UK, which is one of the
complaints we have in the UK. But +/- 6% could actually be beneficial, if
it is correct.

I will be measuring at the incoming terminals some time soon. For now I
have added a variac, which has lengthened  the time I can hold my fingers
on the 8970B from 2 seconds to 9 seconds!!! So a very marked difference in
heatsink temperature since dropping the voltage.

Dave

On 2 January 2017 at 18:14, Poul-Henning Kamp <phk@phk.freebsd.dk> wrote: > -------- > In message <CAJ_qRvb6-79y99aFgAUowZjJcEUK4LWeAEHwDgR > qNOsGQVzneQ@mail.gmail.com> > , Tim Shoppa writes: > > >What modern loads are actually sensitive to high (say, +10 to +20%) line > >voltage? > > In EU you're supposed to have 230V +/- 6% in your outlet. > > The way this was arrived at was: > > A lot of europe used 220V +/- 10% = [198..242] V > > Brittain used 240V +/- 10% = [216..264] V > > Take the average of the two, and use the low max and high min as limits > > QED: 230V +/- 6% = [216..244] > Do you have a reference to this +6%? I've heard from various sources that the UK is 230 -6%/+10%. If the EU dictates otherwise, then I'm certainly over the 6% limit. I may or may not be over the 10% limit. While the UK is still in the EU, it would be good to get this resolved, since we will be leaving in just over 2 years. Rules in Brussels override those made in the UK, which is one of the complaints we have in the UK. But +/- 6% could actually be beneficial, if it is correct. I will be measuring at the incoming terminals some time soon. For now I have added a variac, which has lengthened the time I can hold my fingers on the 8970B from 2 seconds to 9 seconds!!! So a very marked difference in heatsink temperature since dropping the voltage. Dave
AM
Artek Manuals
Tue, Jan 3, 2017 4:41 PM

Vlad

do you have that data for a longer period of time...say 3 to 6 months?

Dave

On 1/3/2017 11:05 AM, Vlad wrote:

Speaking about MAIN... I was interesting to see if "leap second" event
has correlation with MAIN frequency fluctuation

Here is graphs for the MAIN periods recorded. Note: The data on the
charts is "smoothed" by Bezier curves

I could see some "surge" which starts to climb in December 30 and end
at Dec 31 at the time close to the "leap second" event. But not sharp.

For 16-12-29 00:00 to 17-01-02 00:00
http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png

For Dec 31:
http://www.patoka.ca/OCXO/60hz-periods-Dec31.png

It will be interesting to see/compare if anybody else has similar stats.

Regards,
Vlad

On 2017-01-02 13:00, Tim Shoppa wrote:

What modern loads are actually sensitive to high (say, +10 to +20%) line
voltage?

Old incandescent light bulbs were among the most sensitive loads in the
past (so much so, that 130V light bulbs were commonly available from the
industrial suppliers).

I would naively expect the modern CFL's and LED replacements to be fine
with higher line voltage because they have their own built-in switching
regulation.

A lot of modern electronic equipment with switching supplies, are
just fine
at +20% line voltage and may even run cooler.

Tim N3QE

On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom time@radio.sent.com wrote:

There are a couple of recent threads concerning the power line mains
voltage standards. After a bit of research and thinking, I have found
that this is a complex topic. The simple answer is:

  • The standard in the US for the past 50 years has been 120/240 V
    +/- 5%
    RMS at the service entrance to the building. This is a range of
    114/228 V to 126/252 V.
  • The load voltage could be as low as 110/220 V and as high as
    125/250 V
    and be within specifications.

There are two voltage measurement points to consider:

(1) Service voltage: This is the RMS voltage measured at the service
entrance to the building (at the metering point).
(2) Utilization voltage: This is the RMS voltage measured at the load.
It might be measured at an unused socket in a power strip feeding
several pieces of electronic equipment, for example. There are of
course many different utilization voltages present in a home or
business, depending on where you make the measurement.

Most US homes and small businesses are powered by what is commonly
called a "split-phase" 240 V feed. The final distribution system
transformer has a 240 V center-tapped secondary. The center tap is
grounded, and three wires are fed to the building (actually it might be
up to around 6 houses):
(1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L2.
(2) Neutral (white wire) -- This wire is grounded at the distribution
system and at the service entrance to the building.
(3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L1.

Large appliances and HVAC systems are usually connected across L1-L2
(240 V), while most sockets are on circuits either connected across L1-
neutral (120 V) or L2-neutral (120 V).

The voltages I have described are the current standardized values for
the service voltage which have been in general use for about 50 years
(120/240 V +/- 5%). I believe that the original systems installed
before
1940 were designed for a 110/220 V nominal service voltage, but after a
report in 1949 the nominal service voltage was increased to 117/234 V,
as specified in ANSI C84.1-1954. After research in actual buildings, in
the 1960's the nominal service voltage was increased again, to
120/240 V
in the ANSI C84.1-1970 standard. The purpose is to keep the utilization
voltage at the load above 110/220 V.

The voltage at the service entrance should in most cases be in Range A
(120/240V +/-5%). On each 120V leg the service voltage should therefore
be between 114 and 126 V. The utilization voltage at the load should be
between 110 and 125 V due to losses in building wiring.

See details of the current specifications at:

http://www.pge.com/includes/docs/pdfs/mybusiness/
customerservice/energystatus/powerquality/voltage_tolerance.pdf

These voltage specifications were designed for resistive loads and
measurement of the true RMS voltage. In most electronic equipment built
over the past 50 years, the power supply input circuitry is basically a
rectifier connected to a smoothing capacitor. This leads to high input
current surges during the peaks of the waveform, so that the peak
voltage is reduced much more by the building wiring resistance than if
the load was resistive for the same power consumption.

So the waveform shape at different utilization locations in a building
(with active equipment loads) may be different, so the voltage measured
by different AC measuring instruments can differ. Many meters are full
wave average measuring but calibrated so they only read RMS voltage
correctly on pure sinewaves. Other meters are true RMS measuring and
will read very close the correct RMS voltage even if the waveform is
distorted.

Bill Byrom N5BB

On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote:

Mark,

CSA have standards for over and under voltage, Typical no more

that 3%

over and 5% under if memory serves me.

This might help (

fia3660-voltagedropcalc.pdf

)

The power companies here in Alberta are generally good about fixing

problems with line regulation.

There can be problems with industrial areas and big welders or motors
staring as I am sure you know.

I am sure they do not want the bill for replacing equipment that was

subjected to over voltage.

On UPSs: I am sure you are aware that may of them are not TRUE
sine wave
so the DMM may not read correctly.

Mitch


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
Dave
Manuals@ArtekManuals.com
www.ArtekManuals.com


This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

Vlad do you have that data for a longer period of time...say 3 to 6 months? Dave On 1/3/2017 11:05 AM, Vlad wrote: > > > Speaking about MAIN... I was interesting to see if "leap second" event > has correlation with MAIN frequency fluctuation > > Here is graphs for the MAIN periods recorded. Note: The data on the > charts is "smoothed" by Bezier curves > > I could see some "surge" which starts to climb in December 30 and end > at Dec 31 at the time close to the "leap second" event. But not sharp. > > For 16-12-29 00:00 to 17-01-02 00:00 > http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png > > > For Dec 31: > http://www.patoka.ca/OCXO/60hz-periods-Dec31.png > > > It will be interesting to see/compare if anybody else has similar stats. > > Regards, > Vlad > > > On 2017-01-02 13:00, Tim Shoppa wrote: >> What modern loads are actually sensitive to high (say, +10 to +20%) line >> voltage? >> >> Old incandescent light bulbs were among the most sensitive loads in the >> past (so much so, that 130V light bulbs were commonly available from the >> industrial suppliers). >> >> I would naively expect the modern CFL's and LED replacements to be fine >> with higher line voltage because they have their own built-in switching >> regulation. >> >> A lot of modern electronic equipment with switching supplies, are >> just fine >> at +20% line voltage and may even run cooler. >> >> Tim N3QE >> >> On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom <time@radio.sent.com> wrote: >> >>> There are a couple of recent threads concerning the power line mains >>> voltage standards. After a bit of research and thinking, I have found >>> that this is a complex topic. The simple answer is: >>> >>> >>> * The standard in the US for the past 50 years has been 120/240 V >>> +/- 5% >>> RMS at the service entrance to the building. This is a range of >>> 114/228 V to 126/252 V. >>> * The load voltage could be as low as 110/220 V and as high as >>> 125/250 V >>> and be within specifications. >>> >>> >>> There are two voltage measurement points to consider: >>> >>> (1) Service voltage: This is the RMS voltage measured at the service >>> entrance to the building (at the metering point). >>> (2) Utilization voltage: This is the RMS voltage measured at the load. >>> It might be measured at an unused socket in a power strip feeding >>> several pieces of electronic equipment, for example. There are of >>> course many different utilization voltages present in a home or >>> business, depending on where you make the measurement. >>> >>> >>> Most US homes and small businesses are powered by what is commonly >>> called a "split-phase" 240 V feed. The final distribution system >>> transformer has a 240 V center-tapped secondary. The center tap is >>> grounded, and three wires are fed to the building (actually it might be >>> up to around 6 houses): >>> (1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to the >>> neutral or 240 V to Leg L2. >>> (2) Neutral (white wire) -- This wire is grounded at the distribution >>> system and at the service entrance to the building. >>> (3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the >>> neutral or 240 V to Leg L1. >>> >>> >>> Large appliances and HVAC systems are usually connected across L1-L2 >>> (240 V), while most sockets are on circuits either connected across L1- >>> neutral (120 V) or L2-neutral (120 V). >>> >>> >>> The voltages I have described are the current standardized values for >>> the service voltage which have been in general use for about 50 years >>> (120/240 V +/- 5%). I believe that the original systems installed >>> before >>> 1940 were designed for a 110/220 V nominal service voltage, but after a >>> report in 1949 the nominal service voltage was increased to 117/234 V, >>> as specified in ANSI C84.1-1954. After research in actual buildings, in >>> the 1960's the nominal service voltage was increased again, to >>> 120/240 V >>> in the ANSI C84.1-1970 standard. The purpose is to keep the utilization >>> voltage at the load above 110/220 V. >>> >>> >>> The voltage at the service entrance should in most cases be in Range A >>> (120/240V +/-5%). On each 120V leg the service voltage should therefore >>> be between 114 and 126 V. The utilization voltage at the load should be >>> between 110 and 125 V due to losses in building wiring. >>> >>> >>> See details of the current specifications at: >>> >>> http://www.pge.com/includes/docs/pdfs/mybusiness/ >>> customerservice/energystatus/powerquality/voltage_tolerance.pdf >>> >>> >>> These voltage specifications were designed for resistive loads and >>> measurement of the true RMS voltage. In most electronic equipment built >>> over the past 50 years, the power supply input circuitry is basically a >>> rectifier connected to a smoothing capacitor. This leads to high input >>> current surges during the peaks of the waveform, so that the peak >>> voltage is reduced much more by the building wiring resistance than if >>> the load was resistive for the same power consumption. >>> >>> >>> So the waveform shape at different utilization locations in a building >>> (with active equipment loads) may be different, so the voltage measured >>> by different AC measuring instruments can differ. Many meters are full >>> wave average measuring but calibrated so they only read RMS voltage >>> correctly on pure sinewaves. Other meters are true RMS measuring and >>> will read very close the correct RMS voltage even if the waveform is >>> distorted. >>> -- >>> >>> Bill Byrom N5BB >>> >>> >>> >>> >>> >>> On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote: >>> >>> > Mark, >>> >>> > >>> >>> > CSA have standards for over and under voltage, Typical no more >>> that 3% >>> > over and 5% under if memory serves me. >>> >>> > >>> >>> > This might help ( >>> >>> > http://www.safetyauthority.ca/sites/default/files/csa- >>> fia3660-voltagedropcalc.pdf >>> > ) >>> >>> > The power companies here in Alberta are generally good about fixing >>> >>> > problems with line regulation. >>> >>> > There can be problems with industrial areas and big welders or motors >>> > staring as I am sure you know. >>> >>> > I am sure they do not want the bill for replacing equipment that was >>> >>> > subjected to over voltage. >>> >>> > >>> >>> > On UPSs: I am sure you are aware that may of them are not TRUE >>> > sine wave >>> > so the DMM may not read correctly. >>> >>> > >>> >>> > Mitch >>> >>> >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/ >>> mailman/listinfo/time-nuts >>> and follow the instructions there. >>> >> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to >> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >> and follow the instructions there. > -- Dave Manuals@ArtekManuals.com www.ArtekManuals.com --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus
J
J
Tue, Jan 3, 2017 5:01 PM

Power utilities tweak the system frequency on a daily basis to keep MAINS
powered clocks correct. I wonder what their correction strategy was for the
leap second?

On Tue, Jan 3, 2017 at 11:05 AM, Vlad time@patoka.org wrote:

Speaking about MAIN... I was interesting to see if "leap second" event has
correlation with MAIN frequency fluctuation

Here is graphs for the MAIN periods recorded. Note: The data on the charts
is "smoothed" by Bezier curves

I could see some "surge" which starts to climb in December 30 and end at
Dec 31 at the time close to the "leap second" event. But not sharp.

For 16-12-29 00:00 to 17-01-02 00:00
http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png

For Dec 31:
http://www.patoka.ca/OCXO/60hz-periods-Dec31.png

It will be interesting to see/compare if anybody else has similar stats.

Regards,
Vlad

On 2017-01-02 13:00, Tim Shoppa wrote:

What modern loads are actually sensitive to high (say, +10 to +20%) line
voltage?

Old incandescent light bulbs were among the most sensitive loads in the
past (so much so, that 130V light bulbs were commonly available from the
industrial suppliers).

I would naively expect the modern CFL's and LED replacements to be fine
with higher line voltage because they have their own built-in switching
regulation.

A lot of modern electronic equipment with switching supplies, are just
fine
at +20% line voltage and may even run cooler.

Tim N3QE

On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom time@radio.sent.com wrote:

There are a couple of recent threads concerning the power line mains

voltage standards. After a bit of research and thinking, I have found
that this is a complex topic. The simple answer is:

  • The standard in the US for the past 50 years has been 120/240 V +/- 5%
    RMS at the service entrance to the building. This is a range of
    114/228 V to 126/252 V.
  • The load voltage could be as low as 110/220 V and as high as 125/250 V
    and be within specifications.

There are two voltage measurement points to consider:

(1) Service voltage: This is the RMS voltage measured at the service
entrance to the building (at the metering point).
(2) Utilization voltage: This is the RMS voltage measured at the load.
It might be measured at an unused socket in a power strip feeding
several pieces of electronic equipment, for example. There are of
course many different utilization voltages present in a home or
business, depending on where you make the measurement.

Most US homes and small businesses are powered by what is commonly
called a "split-phase" 240 V feed. The final distribution system
transformer has a 240 V center-tapped secondary. The center tap is
grounded, and three wires are fed to the building (actually it might be
up to around 6 houses):
(1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L2.
(2) Neutral (white wire) -- This wire is grounded at the distribution
system and at the service entrance to the building.
(3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the
neutral or 240 V to Leg L1.

Large appliances and HVAC systems are usually connected across L1-L2
(240 V), while most sockets are on circuits either connected across L1-
neutral (120 V) or L2-neutral (120 V).

The voltages I have described are the current standardized values for
the service voltage which have been in general use for about 50 years
(120/240 V +/- 5%). I believe that the original systems installed before
1940 were designed for a 110/220 V nominal service voltage, but after a
report in 1949 the nominal service voltage was increased to 117/234 V,
as specified in ANSI C84.1-1954. After research in actual buildings, in
the 1960's the nominal service voltage was increased again, to 120/240 V
in the ANSI C84.1-1970 standard. The purpose is to keep the utilization
voltage at the load above 110/220 V.

The voltage at the service entrance should in most cases be in Range A
(120/240V +/-5%). On each 120V leg the service voltage should therefore
be between 114 and 126 V. The utilization voltage at the load should be
between 110 and 125 V due to losses in building wiring.

See details of the current specifications at:

http://www.pge.com/includes/docs/pdfs/mybusiness/
customerservice/energystatus/powerquality/voltage_tolerance.pdf

These voltage specifications were designed for resistive loads and
measurement of the true RMS voltage. In most electronic equipment built
over the past 50 years, the power supply input circuitry is basically a
rectifier connected to a smoothing capacitor. This leads to high input
current surges during the peaks of the waveform, so that the peak
voltage is reduced much more by the building wiring resistance than if
the load was resistive for the same power consumption.

So the waveform shape at different utilization locations in a building
(with active equipment loads) may be different, so the voltage measured
by different AC measuring instruments can differ. Many meters are full
wave average measuring but calibrated so they only read RMS voltage
correctly on pure sinewaves. Other meters are true RMS measuring and
will read very close the correct RMS voltage even if the waveform is
distorted.

Bill Byrom N5BB

On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote:

Mark,

CSA have standards for over and under voltage, Typical no more that 3%
over and 5% under if memory serves me.

This might help (

fia3660-voltagedropcalc.pdf

)

The power companies here in Alberta are generally good about fixing

problems with line regulation.

There can be problems with industrial areas and big welders or motors
staring as I am sure you know.

I am sure they do not want the bill for replacing equipment that was

subjected to over voltage.

On UPSs: I am sure you are aware that may of them are not TRUE
sine wave
so the DMM may not read correctly.

Mitch


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/m
ailman/listinfo/time-nuts
and follow the instructions there.

--
WBW,

V.P.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/m
ailman/listinfo/time-nuts
and follow the instructions there.

Power utilities tweak the system frequency on a daily basis to keep MAINS powered clocks correct. I wonder what their correction strategy was for the leap second? On Tue, Jan 3, 2017 at 11:05 AM, Vlad <time@patoka.org> wrote: > > > Speaking about MAIN... I was interesting to see if "leap second" event has > correlation with MAIN frequency fluctuation > > Here is graphs for the MAIN periods recorded. Note: The data on the charts > is "smoothed" by Bezier curves > > I could see some "surge" which starts to climb in December 30 and end at > Dec 31 at the time close to the "leap second" event. But not sharp. > > For 16-12-29 00:00 to 17-01-02 00:00 > http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png > > > For Dec 31: > http://www.patoka.ca/OCXO/60hz-periods-Dec31.png > > > It will be interesting to see/compare if anybody else has similar stats. > > Regards, > Vlad > > > On 2017-01-02 13:00, Tim Shoppa wrote: > >> What modern loads are actually sensitive to high (say, +10 to +20%) line >> voltage? >> >> Old incandescent light bulbs were among the most sensitive loads in the >> past (so much so, that 130V light bulbs were commonly available from the >> industrial suppliers). >> >> I would naively expect the modern CFL's and LED replacements to be fine >> with higher line voltage because they have their own built-in switching >> regulation. >> >> A lot of modern electronic equipment with switching supplies, are just >> fine >> at +20% line voltage and may even run cooler. >> >> Tim N3QE >> >> On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom <time@radio.sent.com> wrote: >> >> There are a couple of recent threads concerning the power line mains >>> voltage standards. After a bit of research and thinking, I have found >>> that this is a complex topic. The simple answer is: >>> >>> >>> * The standard in the US for the past 50 years has been 120/240 V +/- 5% >>> RMS at the service entrance to the building. This is a range of >>> 114/228 V to 126/252 V. >>> * The load voltage could be as low as 110/220 V and as high as 125/250 V >>> and be within specifications. >>> >>> >>> There are two voltage measurement points to consider: >>> >>> (1) Service voltage: This is the RMS voltage measured at the service >>> entrance to the building (at the metering point). >>> (2) Utilization voltage: This is the RMS voltage measured at the load. >>> It might be measured at an unused socket in a power strip feeding >>> several pieces of electronic equipment, for example. There are of >>> course many different utilization voltages present in a home or >>> business, depending on where you make the measurement. >>> >>> >>> Most US homes and small businesses are powered by what is commonly >>> called a "split-phase" 240 V feed. The final distribution system >>> transformer has a 240 V center-tapped secondary. The center tap is >>> grounded, and three wires are fed to the building (actually it might be >>> up to around 6 houses): >>> (1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to the >>> neutral or 240 V to Leg L2. >>> (2) Neutral (white wire) -- This wire is grounded at the distribution >>> system and at the service entrance to the building. >>> (3) Leg L2 phase B (black wire) -- This wire will measure 120 V to the >>> neutral or 240 V to Leg L1. >>> >>> >>> Large appliances and HVAC systems are usually connected across L1-L2 >>> (240 V), while most sockets are on circuits either connected across L1- >>> neutral (120 V) or L2-neutral (120 V). >>> >>> >>> The voltages I have described are the current standardized values for >>> the service voltage which have been in general use for about 50 years >>> (120/240 V +/- 5%). I believe that the original systems installed before >>> 1940 were designed for a 110/220 V nominal service voltage, but after a >>> report in 1949 the nominal service voltage was increased to 117/234 V, >>> as specified in ANSI C84.1-1954. After research in actual buildings, in >>> the 1960's the nominal service voltage was increased again, to 120/240 V >>> in the ANSI C84.1-1970 standard. The purpose is to keep the utilization >>> voltage at the load above 110/220 V. >>> >>> >>> The voltage at the service entrance should in most cases be in Range A >>> (120/240V +/-5%). On each 120V leg the service voltage should therefore >>> be between 114 and 126 V. The utilization voltage at the load should be >>> between 110 and 125 V due to losses in building wiring. >>> >>> >>> See details of the current specifications at: >>> >>> http://www.pge.com/includes/docs/pdfs/mybusiness/ >>> customerservice/energystatus/powerquality/voltage_tolerance.pdf >>> >>> >>> These voltage specifications were designed for resistive loads and >>> measurement of the true RMS voltage. In most electronic equipment built >>> over the past 50 years, the power supply input circuitry is basically a >>> rectifier connected to a smoothing capacitor. This leads to high input >>> current surges during the peaks of the waveform, so that the peak >>> voltage is reduced much more by the building wiring resistance than if >>> the load was resistive for the same power consumption. >>> >>> >>> So the waveform shape at different utilization locations in a building >>> (with active equipment loads) may be different, so the voltage measured >>> by different AC measuring instruments can differ. Many meters are full >>> wave average measuring but calibrated so they only read RMS voltage >>> correctly on pure sinewaves. Other meters are true RMS measuring and >>> will read very close the correct RMS voltage even if the waveform is >>> distorted. >>> -- >>> >>> Bill Byrom N5BB >>> >>> >>> >>> >>> >>> On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote: >>> >>> > Mark, >>> >>> > >>> >>> > CSA have standards for over and under voltage, Typical no more that 3% >>> > over and 5% under if memory serves me. >>> >>> > >>> >>> > This might help ( >>> >>> > http://www.safetyauthority.ca/sites/default/files/csa- >>> fia3660-voltagedropcalc.pdf >>> > ) >>> >>> > The power companies here in Alberta are generally good about fixing >>> >>> > problems with line regulation. >>> >>> > There can be problems with industrial areas and big welders or motors >>> > staring as I am sure you know. >>> >>> > I am sure they do not want the bill for replacing equipment that was >>> >>> > subjected to over voltage. >>> >>> > >>> >>> > On UPSs: I am sure you are aware that may of them are not TRUE >>> > sine wave >>> > so the DMM may not read correctly. >>> >>> > >>> >>> > Mitch >>> >>> >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to https://www.febo.com/cgi-bin/ >>> mailman/listinfo/time-nuts >>> and follow the instructions there. >>> >>> _______________________________________________ >> time-nuts mailing list -- time-nuts@febo.com >> To unsubscribe, go to https://www.febo.com/cgi-bin/m >> ailman/listinfo/time-nuts >> and follow the instructions there. >> > > -- > WBW, > > V.P. > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/m > ailman/listinfo/time-nuts > and follow the instructions there. >
V
Vlad
Tue, Jan 3, 2017 5:29 PM

I put some raw data here:

http://www.patoka.ca/OCXO/60HZ.logs.tar.Z

Unfortunately its not continuous, because of for some period of times my
machine was offline (software upgrades or my radio made some mess with
RF which affects the MCU and recordings. And I was busy with something
else to check what was going on there...

The format is very simple:

[Time Stamp]            [Period]              [1/9830400]

16-12-05 22:00:56.683 [-] 0.01667439778643      163916  -49
16-12-05 22:02:04.976 [-] 0.01667348225909      163907  +9
16-12-05 22:03:13.253 [-] 0.01666941324869      163867  +40

The column [-/+/0] just indicate if periods is up or down from the
"golden standard"
The [1/9830400] - is the what the timer(counter) value was
and the last column is just a delta with previous measurement

Note: the device itself catch each and every zero-cross event 8192
times, and then do averaging (simple shift to the right the big counter
value). Then it took this averaged value, translate it to main periods
and prints the results as [Period]

Regards,
Vlad

On 2017-01-03 11:41, Artek Manuals wrote:

Vlad

do you have that data for a longer period of time...say 3 to 6 months?

Dave

On 1/3/2017 11:05 AM, Vlad wrote:

Speaking about MAIN... I was interesting to see if "leap second" event
has correlation with MAIN frequency fluctuation

Here is graphs for the MAIN periods recorded. Note: The data on the
charts is "smoothed" by Bezier curves

I could see some "surge" which starts to climb in December 30 and end
at Dec 31 at the time close to the "leap second" event. But not sharp.

For 16-12-29 00:00 to 17-01-02 00:00
http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png

For Dec 31:
http://www.patoka.ca/OCXO/60hz-periods-Dec31.png

It will be interesting to see/compare if anybody else has similar
stats.

Regards,
Vlad

On 2017-01-02 13:00, Tim Shoppa wrote:

What modern loads are actually sensitive to high (say, +10 to +20%)
line
voltage?

Old incandescent light bulbs were among the most sensitive loads in
the
past (so much so, that 130V light bulbs were commonly available from
the
industrial suppliers).

I would naively expect the modern CFL's and LED replacements to be
fine
with higher line voltage because they have their own built-in
switching
regulation.

A lot of modern electronic equipment with switching supplies, are
just fine
at +20% line voltage and may even run cooler.

Tim N3QE

On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom time@radio.sent.com
wrote:

There are a couple of recent threads concerning the power line mains
voltage standards. After a bit of research and thinking, I have
found
that this is a complex topic. The simple answer is:

  • The standard in the US for the past 50 years has been 120/240 V
    +/- 5%
    RMS at the service entrance to the building. This is a range of
    114/228 V to 126/252 V.
  • The load voltage could be as low as 110/220 V and as high as
    125/250 V
    and be within specifications.

There are two voltage measurement points to consider:

(1) Service voltage: This is the RMS voltage measured at the service
entrance to the building (at the metering point).
(2) Utilization voltage: This is the RMS voltage measured at the
load.
It might be measured at an unused socket in a power strip
feeding
several pieces of electronic equipment, for example. There are
of
course many different utilization voltages present in a home or
business, depending on where you make the measurement.

Most US homes and small businesses are powered by what is commonly
called a "split-phase" 240 V feed. The final distribution system
transformer has a 240 V center-tapped secondary. The center tap is
grounded, and three wires are fed to the building (actually it might
be
up to around 6 houses):
(1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to
the
neutral or 240 V to Leg L2.
(2) Neutral (white wire) -- This wire is grounded at the
distribution
system and at the service entrance to the building.
(3) Leg L2 phase B (black wire) -- This wire will measure 120 V to
the
neutral or 240 V to Leg L1.

Large appliances and HVAC systems are usually connected across L1-L2
(240 V), while most sockets are on circuits either connected across
L1-
neutral (120 V) or L2-neutral (120 V).

The voltages I have described are the current standardized values
for
the service voltage which have been in general use for about 50
years
(120/240 V +/- 5%). I believe that the original systems installed
before
1940 were designed for a 110/220 V nominal service voltage, but
after a
report in 1949 the nominal service voltage was increased to 117/234
V,
as specified in ANSI C84.1-1954. After research in actual buildings,
in
the 1960's the nominal service voltage was increased again, to
120/240 V
in the ANSI C84.1-1970 standard. The purpose is to keep the
utilization
voltage at the load above 110/220 V.

The voltage at the service entrance should in most cases be in Range
A
(120/240V +/-5%). On each 120V leg the service voltage should
therefore
be between 114 and 126 V. The utilization voltage at the load should
be
between 110 and 125 V due to losses in building wiring.

See details of the current specifications at:

http://www.pge.com/includes/docs/pdfs/mybusiness/
customerservice/energystatus/powerquality/voltage_tolerance.pdf

These voltage specifications were designed for resistive loads and
measurement of the true RMS voltage. In most electronic equipment
built
over the past 50 years, the power supply input circuitry is
basically a
rectifier connected to a smoothing capacitor. This leads to high
input
current surges during the peaks of the waveform, so that the peak
voltage is reduced much more by the building wiring resistance than
if
the load was resistive for the same power consumption.

So the waveform shape at different utilization locations in a
building
(with active equipment loads) may be different, so the voltage
measured
by different AC measuring instruments can differ. Many meters are
full
wave average measuring but calibrated so they only read RMS voltage
correctly on pure sinewaves. Other meters are true RMS measuring and
will read very close the correct RMS voltage even if the waveform is
distorted.
-- Bill Byrom N5BB

On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote:

Mark,

CSA have standards for over and under voltage, Typical no more that 3%
over and 5% under if memory serves me.

This might help (

fia3660-voltagedropcalc.pdf

)

The power companies here in Alberta are generally good about fixing

problems with line regulation.

There can be problems with industrial areas and big welders or motors
staring as I am sure you know.

I am sure they do not want the bill for replacing equipment that was

subjected to over voltage.

On UPSs: I am sure you are aware that may of them are not TRUE
sine wave
so the DMM may not read correctly.

Mitch


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/
mailman/listinfo/time-nuts
and follow the instructions there.


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

--
WBW,

V.P.

I put some raw data here: http://www.patoka.ca/OCXO/60HZ.logs.tar.Z Unfortunately its not continuous, because of for some period of times my machine was offline (software upgrades or my radio made some mess with RF which affects the MCU and recordings. And I was busy with something else to check what was going on there... The format is very simple: # [Time Stamp] [Period] [1/9830400] 16-12-05 22:00:56.683 [-] 0.01667439778643 163916 -49 16-12-05 22:02:04.976 [-] 0.01667348225909 163907 +9 16-12-05 22:03:13.253 [-] 0.01666941324869 163867 +40 The column [-/+/0] just indicate if periods is up or down from the "golden standard" The [1/9830400] - is the what the timer(counter) value was and the last column is just a delta with previous measurement Note: the device itself catch each and every zero-cross event 8192 times, and then do averaging (simple shift to the right the big counter value). Then it took this averaged value, translate it to main periods and prints the results as [Period] Regards, Vlad On 2017-01-03 11:41, Artek Manuals wrote: > Vlad > > do you have that data for a longer period of time...say 3 to 6 months? > > Dave > > > > On 1/3/2017 11:05 AM, Vlad wrote: >> >> >> Speaking about MAIN... I was interesting to see if "leap second" event >> has correlation with MAIN frequency fluctuation >> >> Here is graphs for the MAIN periods recorded. Note: The data on the >> charts is "smoothed" by Bezier curves >> >> I could see some "surge" which starts to climb in December 30 and end >> at Dec 31 at the time close to the "leap second" event. But not sharp. >> >> For 16-12-29 00:00 to 17-01-02 00:00 >> http://www.patoka.ca/OCXO/60hz-periods-Dec29-Jan2.png >> >> >> For Dec 31: >> http://www.patoka.ca/OCXO/60hz-periods-Dec31.png >> >> >> It will be interesting to see/compare if anybody else has similar >> stats. >> >> Regards, >> Vlad >> >> >> On 2017-01-02 13:00, Tim Shoppa wrote: >>> What modern loads are actually sensitive to high (say, +10 to +20%) >>> line >>> voltage? >>> >>> Old incandescent light bulbs were among the most sensitive loads in >>> the >>> past (so much so, that 130V light bulbs were commonly available from >>> the >>> industrial suppliers). >>> >>> I would naively expect the modern CFL's and LED replacements to be >>> fine >>> with higher line voltage because they have their own built-in >>> switching >>> regulation. >>> >>> A lot of modern electronic equipment with switching supplies, are >>> just fine >>> at +20% line voltage and may even run cooler. >>> >>> Tim N3QE >>> >>> On Sun, Jan 1, 2017 at 11:49 PM, Bill Byrom <time@radio.sent.com> >>> wrote: >>> >>>> There are a couple of recent threads concerning the power line mains >>>> voltage standards. After a bit of research and thinking, I have >>>> found >>>> that this is a complex topic. The simple answer is: >>>> >>>> >>>> * The standard in the US for the past 50 years has been 120/240 V >>>> +/- 5% >>>> RMS at the service entrance to the building. This is a range of >>>> 114/228 V to 126/252 V. >>>> * The load voltage could be as low as 110/220 V and as high as >>>> 125/250 V >>>> and be within specifications. >>>> >>>> >>>> There are two voltage measurement points to consider: >>>> >>>> (1) Service voltage: This is the RMS voltage measured at the service >>>> entrance to the building (at the metering point). >>>> (2) Utilization voltage: This is the RMS voltage measured at the >>>> load. >>>> It might be measured at an unused socket in a power strip >>>> feeding >>>> several pieces of electronic equipment, for example. There are >>>> of >>>> course many different utilization voltages present in a home or >>>> business, depending on where you make the measurement. >>>> >>>> >>>> Most US homes and small businesses are powered by what is commonly >>>> called a "split-phase" 240 V feed. The final distribution system >>>> transformer has a 240 V center-tapped secondary. The center tap is >>>> grounded, and three wires are fed to the building (actually it might >>>> be >>>> up to around 6 houses): >>>> (1) Leg L1 or phase A (red wire) -- This wire will measure 120 V to >>>> the >>>> neutral or 240 V to Leg L2. >>>> (2) Neutral (white wire) -- This wire is grounded at the >>>> distribution >>>> system and at the service entrance to the building. >>>> (3) Leg L2 phase B (black wire) -- This wire will measure 120 V to >>>> the >>>> neutral or 240 V to Leg L1. >>>> >>>> >>>> Large appliances and HVAC systems are usually connected across L1-L2 >>>> (240 V), while most sockets are on circuits either connected across >>>> L1- >>>> neutral (120 V) or L2-neutral (120 V). >>>> >>>> >>>> The voltages I have described are the current standardized values >>>> for >>>> the service voltage which have been in general use for about 50 >>>> years >>>> (120/240 V +/- 5%). I believe that the original systems installed >>>> before >>>> 1940 were designed for a 110/220 V nominal service voltage, but >>>> after a >>>> report in 1949 the nominal service voltage was increased to 117/234 >>>> V, >>>> as specified in ANSI C84.1-1954. After research in actual buildings, >>>> in >>>> the 1960's the nominal service voltage was increased again, to >>>> 120/240 V >>>> in the ANSI C84.1-1970 standard. The purpose is to keep the >>>> utilization >>>> voltage at the load above 110/220 V. >>>> >>>> >>>> The voltage at the service entrance should in most cases be in Range >>>> A >>>> (120/240V +/-5%). On each 120V leg the service voltage should >>>> therefore >>>> be between 114 and 126 V. The utilization voltage at the load should >>>> be >>>> between 110 and 125 V due to losses in building wiring. >>>> >>>> >>>> See details of the current specifications at: >>>> >>>> http://www.pge.com/includes/docs/pdfs/mybusiness/ >>>> customerservice/energystatus/powerquality/voltage_tolerance.pdf >>>> >>>> >>>> These voltage specifications were designed for resistive loads and >>>> measurement of the true RMS voltage. In most electronic equipment >>>> built >>>> over the past 50 years, the power supply input circuitry is >>>> basically a >>>> rectifier connected to a smoothing capacitor. This leads to high >>>> input >>>> current surges during the peaks of the waveform, so that the peak >>>> voltage is reduced much more by the building wiring resistance than >>>> if >>>> the load was resistive for the same power consumption. >>>> >>>> >>>> So the waveform shape at different utilization locations in a >>>> building >>>> (with active equipment loads) may be different, so the voltage >>>> measured >>>> by different AC measuring instruments can differ. Many meters are >>>> full >>>> wave average measuring but calibrated so they only read RMS voltage >>>> correctly on pure sinewaves. Other meters are true RMS measuring and >>>> will read very close the correct RMS voltage even if the waveform is >>>> distorted. >>>> -- Bill Byrom N5BB >>>> >>>> >>>> >>>> >>>> >>>> On Sun, Jan 1, 2017, at 12:16 PM, CIW308 VE6OH wrote: >>>> >>>> > Mark, >>>> >>>> > >>>> >>>> > CSA have standards for over and under voltage, Typical no more that 3% >>>> > over and 5% under if memory serves me. >>>> >>>> > >>>> >>>> > This might help ( >>>> >>>> > http://www.safetyauthority.ca/sites/default/files/csa- >>>> fia3660-voltagedropcalc.pdf >>>> > ) >>>> >>>> > The power companies here in Alberta are generally good about fixing >>>> >>>> > problems with line regulation. >>>> >>>> > There can be problems with industrial areas and big welders or motors >>>> > staring as I am sure you know. >>>> >>>> > I am sure they do not want the bill for replacing equipment that was >>>> >>>> > subjected to over voltage. >>>> >>>> > >>>> >>>> > On UPSs: I am sure you are aware that may of them are not TRUE >>>> > sine wave >>>> > so the DMM may not read correctly. >>>> >>>> > >>>> >>>> > Mitch >>>> >>>> >>>> _______________________________________________ >>>> time-nuts mailing list -- time-nuts@febo.com >>>> To unsubscribe, go to https://www.febo.com/cgi-bin/ >>>> mailman/listinfo/time-nuts >>>> and follow the instructions there. >>>> >>> _______________________________________________ >>> time-nuts mailing list -- time-nuts@febo.com >>> To unsubscribe, go to >>> https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts >>> and follow the instructions there. >> -- WBW, V.P.
DD
Dr. David Kirkby (Kirkby Microwave Ltd)
Tue, Jan 3, 2017 6:50 PM

On 2 January 2017 at 05:15, Jeremy Nichols jn6wfo@gmail.com wrote:

Thank you for the detailed analysis, Bill. The voltage measurements I made
in my garage laboratory were duplicated by the utility with their meter,
which was connected at the service entrance.

I have just been chatting to a friend who was a controller at two power
stations in the UK - Darlington (coal) and Bradwell (nuclear). He tells me
that the voltage is likely to be higher in the summer around 2-3 am in the
morning. Now it might seem obvious that the load is smaller in summer than
in the middle of winter, but this is NOT the reason the voltage rises more
in summer. I must admit though, I could still not understand it, and he
admits he could not explain it, but just tells me it is so. But a few
things I did get, which are not all obvious - some are.

  1. The real power consumed by the users + losses must balance the power
    generated. That's pretty obvious.

  2. The reactive power (V*A) must also balance - perhaps less obvious.

  3. The voltage generated by a generator when it is not providing any load
    is controlled by the current in the field winding.

  4. Before connecting a generator to the grid it is necessary to ensure the
    voltage and phases are matched.

  5. Once the generator is on the grid, there's nothing the generator can do
    that has any practical effect on the voltage. Even with a nuclear power
    station, the output power it is a small fraction of the overall power being
    generated by the all the power stations, so one power station coming on/off
    line does not have any significant effect on the voltage of the grid.

  6. What the operator can do is

  • Generator more power, by increasing the steam that drivers the generator.
  • Change the reactive power by changing the field current
  1. As soon as the generator is connector, he would increase the steam to
    provide at least  5 MW at Bradwell (nuclear, 2 MW at Darlington (coal), as
    failing to do so risks the generator going unstable due to disturbances on
    the grid.  This could easily result in the generator becoming a motor,
    which is not good. So there's a minimum power a generator can practically
    provide - in his case 2 or 5 MW.

  2. If there were no uses on the grid, so nobody using any electricity, the
    capacitance of the cables would make the load capacitive.

  3. Users are generally inductive, so in practice the current lags the
    voltage, as the reactive power of users is greater than the the grid.

  4. The higher power usage in winter means that the power factor is further
    from 1.0.

I get the feeling that the voltage might go up more in summer as the
generator are running closer to a point of instability, with small changes
in load causes significantly more change in power factor than in the
winter.

As I say, I never really seemed to get to the bottom of fully understanding
this, but he assures me that voltages will be less stable at light load
than at heavy load.

I guess if I do report a problem, I will get them to measure all 3 phases.
That must increase the chances of at least one phase going outside
specification. I am rugulary going over 250 V, but not 10% more which would
be 253 V.

Dave

On 2 January 2017 at 05:15, Jeremy Nichols <jn6wfo@gmail.com> wrote: > Thank you for the detailed analysis, Bill. The voltage measurements I made > in my garage laboratory were duplicated by the utility with their meter, > which was connected at the service entrance. I have just been chatting to a friend who was a controller at two power stations in the UK - Darlington (coal) and Bradwell (nuclear). He tells me that the voltage is likely to be higher in the summer around 2-3 am in the morning. Now it might seem obvious that the load is smaller in summer than in the middle of winter, but this is NOT the reason the voltage rises more in summer. I must admit though, I could still not understand it, and he admits he could not explain it, but just tells me it is so. But a few things I did get, which are not all obvious - some are. 1) The real power consumed by the users + losses must balance the power generated. That's pretty obvious. 2) The reactive power (V*A) must also balance - perhaps less obvious. 3) The voltage generated by a generator when it is not providing any load is controlled by the current in the field winding. 4) Before connecting a generator to the grid it is necessary to ensure the voltage and phases are matched. 5) Once the generator is on the grid, there's nothing the generator can do that has any practical effect on the voltage. Even with a nuclear power station, the output power it is a small fraction of the overall power being generated by the all the power stations, so one power station coming on/off line does not have any significant effect on the voltage of the grid. 6) What the operator can do is * Generator more power, by increasing the steam that drivers the generator. * Change the reactive power by changing the field current 7) As soon as the generator is connector, he would increase the steam to provide at least 5 MW at Bradwell (nuclear, 2 MW at Darlington (coal), as failing to do so risks the generator going unstable due to disturbances on the grid. This could easily result in the generator becoming a motor, which is not good. So there's a minimum power a generator can practically provide - in his case 2 or 5 MW. 8) If there were no uses on the grid, so nobody using any electricity, the capacitance of the cables would make the load capacitive. 9) Users are generally inductive, so in practice the current lags the voltage, as the reactive power of users is greater than the the grid. 10) The higher power usage in winter means that the power factor is further from 1.0. I get the feeling that the voltage might go up more in summer as the generator are running closer to a point of instability, with small changes in load causes significantly more change in power factor than in the winter. As I say, I never really seemed to get to the bottom of fully understanding this, but he assures me that voltages will be less stable at light load than at heavy load. I guess if I do report a problem, I will get them to measure all 3 phases. That must increase the chances of at least one phase going outside specification. I am rugulary going over 250 V, but not 10% more which would be 253 V. Dave
BC
Bob Camp
Tue, Jan 3, 2017 7:08 PM

Hi

Measuring line voltage for “official” purposes straight up with a lab grade device that may
have a bandwidth of many KHz (or even 100’s of KHz) is generally not a good way to go.
The line voltage is the value of the fundamental (50 or 60 Hz) sine wave. All the other nonsense
that accumulates is more likely load related than line related. If the power company brings
out the right stuff, it looks more like a spectrum analyzer inside than a normal voltmeter. They
sell a lot of 24 bit audio DAC’s into that sort of gear. Team them up with some DSP and you
get all sorts of interesting data. The “one number” that counts is the fundamental ….

Bob

On Jan 3, 2017, at 1:50 PM, Dr. David Kirkby (Kirkby Microwave Ltd) drkirkby@kirkbymicrowave.co.uk wrote:

On 2 January 2017 at 05:15, Jeremy Nichols jn6wfo@gmail.com wrote:

Thank you for the detailed analysis, Bill. The voltage measurements I made
in my garage laboratory were duplicated by the utility with their meter,
which was connected at the service entrance.

I have just been chatting to a friend who was a controller at two power
stations in the UK - Darlington (coal) and Bradwell (nuclear). He tells me
that the voltage is likely to be higher in the summer around 2-3 am in the
morning. Now it might seem obvious that the load is smaller in summer than
in the middle of winter, but this is NOT the reason the voltage rises more
in summer. I must admit though, I could still not understand it, and he
admits he could not explain it, but just tells me it is so. But a few
things I did get, which are not all obvious - some are.

  1. The real power consumed by the users + losses must balance the power
    generated. That's pretty obvious.

  2. The reactive power (V*A) must also balance - perhaps less obvious.

  3. The voltage generated by a generator when it is not providing any load
    is controlled by the current in the field winding.

  4. Before connecting a generator to the grid it is necessary to ensure the
    voltage and phases are matched.

  5. Once the generator is on the grid, there's nothing the generator can do
    that has any practical effect on the voltage. Even with a nuclear power
    station, the output power it is a small fraction of the overall power being
    generated by the all the power stations, so one power station coming on/off
    line does not have any significant effect on the voltage of the grid.

  6. What the operator can do is

  • Generator more power, by increasing the steam that drivers the generator.
  • Change the reactive power by changing the field current
  1. As soon as the generator is connector, he would increase the steam to
    provide at least  5 MW at Bradwell (nuclear, 2 MW at Darlington (coal), as
    failing to do so risks the generator going unstable due to disturbances on
    the grid.  This could easily result in the generator becoming a motor,
    which is not good. So there's a minimum power a generator can practically
    provide - in his case 2 or 5 MW.

  2. If there were no uses on the grid, so nobody using any electricity, the
    capacitance of the cables would make the load capacitive.

  3. Users are generally inductive, so in practice the current lags the
    voltage, as the reactive power of users is greater than the the grid.

  4. The higher power usage in winter means that the power factor is further
    from 1.0.

I get the feeling that the voltage might go up more in summer as the
generator are running closer to a point of instability, with small changes
in load causes significantly more change in power factor than in the
winter.

As I say, I never really seemed to get to the bottom of fully understanding
this, but he assures me that voltages will be less stable at light load
than at heavy load.

I guess if I do report a problem, I will get them to measure all 3 phases.
That must increase the chances of at least one phase going outside
specification. I am rugulary going over 250 V, but not 10% more which would
be 253 V.

Dave


time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Hi Measuring line voltage for “official” purposes straight up with a lab grade device that may have a bandwidth of many KHz (or even 100’s of KHz) is generally not a good way to go. The line voltage is the value of the fundamental (50 or 60 Hz) sine wave. All the other nonsense that accumulates is more likely load related than line related. If the power company brings out the right stuff, it looks more like a spectrum analyzer inside than a normal voltmeter. They sell a lot of 24 bit audio DAC’s into that sort of gear. Team them up with some DSP and you get all sorts of interesting data. The “one number” that counts is the fundamental …. Bob > On Jan 3, 2017, at 1:50 PM, Dr. David Kirkby (Kirkby Microwave Ltd) <drkirkby@kirkbymicrowave.co.uk> wrote: > > On 2 January 2017 at 05:15, Jeremy Nichols <jn6wfo@gmail.com> wrote: > >> Thank you for the detailed analysis, Bill. The voltage measurements I made >> in my garage laboratory were duplicated by the utility with their meter, >> which was connected at the service entrance. > > > I have just been chatting to a friend who was a controller at two power > stations in the UK - Darlington (coal) and Bradwell (nuclear). He tells me > that the voltage is likely to be higher in the summer around 2-3 am in the > morning. Now it might seem obvious that the load is smaller in summer than > in the middle of winter, but this is NOT the reason the voltage rises more > in summer. I must admit though, I could still not understand it, and he > admits he could not explain it, but just tells me it is so. But a few > things I did get, which are not all obvious - some are. > > 1) The real power consumed by the users + losses must balance the power > generated. That's pretty obvious. > > 2) The reactive power (V*A) must also balance - perhaps less obvious. > > 3) The voltage generated by a generator when it is not providing any load > is controlled by the current in the field winding. > > 4) Before connecting a generator to the grid it is necessary to ensure the > voltage and phases are matched. > > 5) Once the generator is on the grid, there's nothing the generator can do > that has any practical effect on the voltage. Even with a nuclear power > station, the output power it is a small fraction of the overall power being > generated by the all the power stations, so one power station coming on/off > line does not have any significant effect on the voltage of the grid. > > 6) What the operator can do is > > * Generator more power, by increasing the steam that drivers the generator. > * Change the reactive power by changing the field current > > > 7) As soon as the generator is connector, he would increase the steam to > provide at least 5 MW at Bradwell (nuclear, 2 MW at Darlington (coal), as > failing to do so risks the generator going unstable due to disturbances on > the grid. This could easily result in the generator becoming a motor, > which is not good. So there's a minimum power a generator can practically > provide - in his case 2 or 5 MW. > > 8) If there were no uses on the grid, so nobody using any electricity, the > capacitance of the cables would make the load capacitive. > > 9) Users are generally inductive, so in practice the current lags the > voltage, as the reactive power of users is greater than the the grid. > > 10) The higher power usage in winter means that the power factor is further > from 1.0. > > I get the feeling that the voltage might go up more in summer as the > generator are running closer to a point of instability, with small changes > in load causes significantly more change in power factor than in the > winter. > > As I say, I never really seemed to get to the bottom of fully understanding > this, but he assures me that voltages will be less stable at light load > than at heavy load. > > I guess if I do report a problem, I will get them to measure all 3 phases. > That must increase the chances of at least one phase going outside > specification. I am rugulary going over 250 V, but not 10% more which would > be 253 V. > > Dave > _______________________________________________ > time-nuts mailing list -- time-nuts@febo.com > To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts > and follow the instructions there.
CH
Chuck Harris
Wed, Jan 4, 2017 3:22 AM

Leap seconds only matter if you are counting seconds.  The power
line isn't.  As long as they keep the frequency near nominal, they
are fine.

-Chuck Harris

J wrote:

Power utilities tweak the system frequency on a daily basis to keep MAINS
powered clocks correct. I wonder what their correction strategy was for the
leap second?

On Tue, Jan 3, 2017 at 11:05 AM, Vlad time@patoka.org wrote:

Leap seconds only matter if you are counting seconds. The power line isn't. As long as they keep the frequency near nominal, they are fine. -Chuck Harris J wrote: > Power utilities tweak the system frequency on a daily basis to keep MAINS > powered clocks correct. I wonder what their correction strategy was for the > leap second? > > On Tue, Jan 3, 2017 at 11:05 AM, Vlad <time@patoka.org> wrote: