You do what you can do...
Clay Autery, KY5G
MONTAC Enterprises
(318) 518-1389
On 7/8/2016 1:27 PM, Tim Shoppa wrote:
Everyone else is talking as if these blips can be protected from, by having
a UPS supplying your precious lab equipment.
I strongly disagree.
Tim N3QE
Tim wrote:
I strongly disagree.
What happens, is you have transformers, fluorescent ballasts, and motors
If you now add a UPS in the vicinity of your lab equipment, and it of
course has a transformer in it, it will likely add to the disruption in a
power glitch.
Both theory and experience show that this is not the usual case. (Note
that certain grounding problems can make it appear initially as if there
are magnetic-field problems, but closer analysis reveals that incorrect
grounding is the actual cause.)
The magnetic fields you describe are very localized and diminish rapidly
as you move away from the source. The shielding normally provided by a
metal (or even metallized plastic) housing is plenty to prevent most
problems of this nature, and moving extremely sensitive circuits a few
inches to a few feet is generally enough to resolve any remaining issues.
If magnetic fields were the main problem, it would be impossible to
build and use stereo systems, televisions, telephones, and any sort of
electronic device that monitors or controls anything. Every time the
refrigerator started up, there would be a huge BANG through the stereo,
TV, radio receivers, and telephone, and all of your shop electronics
would go crazy.
The usual problem is glitches on the on-site AC mains supply, and
properly designed and installed on-line UPS systems do a very fine job
of cleaning that up.
Best regards,
Charles
That has been my experience over the last 25 odd years...
Clay Autery, KY5G
MONTAC Enterprises
(318) 518-1389
On 7/8/2016 5:37 PM, Charles Steinmetz wrote:
The usual problem is glitches on the on-site AC mains supply, and
properly designed and installed on-line UPS systems do a very fine job
of cleaning that up.
Best regards,
Charles
I wonder how well a pair of high voltage transformers wired back to
back with a 60 Hz series resonate LC circuit between them would work
for removing power line glitches. They wouldn't do anything for
voltage regulation unlike a constant voltage transformer though. Time
to break out a couple of plate transformers and try it I guess.
On Fri, 8 Jul 2016 10:18:03 -0700, you wrote:
Hi Bob:
A resonate transformer may solve your problem. I added one to my first computer, See Fig 1.
http://www.prc68.com/I/comp.shtml#SWTP
http://www.prc68.com/I/Images/SWTP-01b.jpg
The oval shaped silver can oil capacitor is connected to a winding on the transformer and resonates at 60 Hz. Think of
it as a filter centered at 60 Hz and as an energy storage device.
This removes line spikes and fills in narrow line drop outs.
https://en.wikipedia.org/wiki/Voltage_regulator#Constant-voltage_transformer
Here are models with capacities of: 300, 600, 1200 & 1800 VA:
http://www.hammondmfg.com/CVR.htm
Just search for "Constant-voltage transformer".
Hi
If you try this, be very careful with the voltage at the junction of the L and the C.
Bob
On Jul 8, 2016, at 9:52 PM, David davidwhess@gmail.com wrote:
I wonder how well a pair of high voltage transformers wired back to
back with a 60 Hz series resonate LC circuit between them would work
for removing power line glitches. They wouldn't do anything for
voltage regulation unlike a constant voltage transformer though. Time
to break out a couple of plate transformers and try it I guess.
On Fri, 8 Jul 2016 10:18:03 -0700, you wrote:
Hi Bob:
A resonate transformer may solve your problem. I added one to my first computer, See Fig 1.
http://www.prc68.com/I/comp.shtml#SWTP
http://www.prc68.com/I/Images/SWTP-01b.jpg
The oval shaped silver can oil capacitor is connected to a winding on the transformer and resonates at 60 Hz. Think of
it as a filter centered at 60 Hz and as an energy storage device.
This removes line spikes and fills in narrow line drop outs.
https://en.wikipedia.org/wiki/Voltage_regulator#Constant-voltage_transformer
Here are models with capacities of: 300, 600, 1200 & 1800 VA:
http://www.hammondmfg.com/CVR.htm
Just search for "Constant-voltage transformer".
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
And I will add a high voltage power resistor to limit the Q.
On Fri, 8 Jul 2016 22:12:53 -0400, you wrote:
Hi
If you try this, be very careful with the voltage at the junction of the L and the C.
Bob
On Jul 8, 2016, at 9:52 PM, David davidwhess@gmail.com wrote:
I wonder how well a pair of high voltage transformers wired back to
back with a 60 Hz series resonate LC circuit between them would work
for removing power line glitches. They wouldn't do anything for
voltage regulation unlike a constant voltage transformer though. Time
to break out a couple of plate transformers and try it I guess.
The minor down side is these resonant transformers acoustically hum and run hot. On the plus side they do clean up any kind of noise on the line.
Rob, NC0B
Sent from my iPad
On Jul 8, 2016, at 1:52 PM, Brooke Clarke brooke@pacific.net wrote:
Hi Bob:
A resonate transformer may solve your problem. I added one to my first computer, See Fig 1.
http://www.prc68.com/I/comp.shtml#SWTP
http://www.prc68.com/I/Images/SWTP-01b.jpg
The oval shaped silver can oil capacitor is connected to a winding on the transformer and resonates at 60 Hz. Think of it as a filter centered at 60 Hz and as an energy storage device.
This removes line spikes and fills in narrow line drop outs.
https://en.wikipedia.org/wiki/Voltage_regulator#Constant-voltage_transformer
Here are models with capacities of: 300, 600, 1200 & 1800 VA:
http://www.hammondmfg.com/CVR.htm
Just search for "Constant-voltage transformer".
--
Have Fun,
Brooke Clarke
http://www.PRC68.com
http://www.end2partygovernment.com/2012Issues.html
The lesser of evils is still evil.
-------- Original Message --------
I hope this isn't too far off topic, as this is having a big impact on my testing.
I decided to run an A/B test on one of my GPSDOs: comparing the phase of the two 10MHz output channels. In the middle of the night, there was a long series of 35ns pops in the phase data. Strangely enough, there was nothing in the data collected directly from the unit involved. The preceding two days we had had a number of switching transients where the lights blinked but nothing shut down. So, putting one and one together, I suspect that a fair percentage of the strange results I've been getting has been power-grid related.
So, what to do? I've been looking at UPS devices, and I don't even understand enough to waste my money on a bad one. The two big questions seem to be "on-line" and "sine wave". Make that three: can I trust the mfgs claims? Is there something affordable that could run a pair of 5370s and maybe another 50W worth of DUTs for up to an hour or two and not be prey to power-line transients? Or would it be more cost effective to somehow monitor the power line for spikes or phase jumps and blow off tests or cut out the offending data? From time to time we get a thread on power-line nuts. Should I have been paying more attention?
GFS GPSDO list:
groups.yahoo.com/neo/groups/GFS-GPSDOs/info
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
--
If this email is spam, report it to
https://support.onlymyemail.com/view/report_spam/ODExMjI6MTg5OTEwNzgwNDpyb2JAbmMwYi5jb206ZGVsaXZlcmVk
Hi
Yes indeed they do run a bit warm. You need a mounting location that gets them out
of the way. Having them somewhere you can bump into them …. not good at all. The
newer “toroid” designs are a bit quieter than the older versions.
Bob
On Jul 9, 2016, at 2:41 AM, Rob Sherwood. rob@nc0b.com wrote:
The minor down side is these resonant transformers acoustically hum and run hot. On the plus side they do clean up any kind of noise on the line.
Rob, NC0B
Sent from my iPad
On Jul 8, 2016, at 1:52 PM, Brooke Clarke brooke@pacific.net wrote:
Hi Bob:
A resonate transformer may solve your problem. I added one to my first computer, See Fig 1.
http://www.prc68.com/I/comp.shtml#SWTP
http://www.prc68.com/I/Images/SWTP-01b.jpg
The oval shaped silver can oil capacitor is connected to a winding on the transformer and resonates at 60 Hz. Think of it as a filter centered at 60 Hz and as an energy storage device.
This removes line spikes and fills in narrow line drop outs.
https://en.wikipedia.org/wiki/Voltage_regulator#Constant-voltage_transformer
Here are models with capacities of: 300, 600, 1200 & 1800 VA:
http://www.hammondmfg.com/CVR.htm
Just search for "Constant-voltage transformer".
--
Have Fun,
Brooke Clarke
http://www.PRC68.com
http://www.end2partygovernment.com/2012Issues.html
The lesser of evils is still evil.
-------- Original Message --------
I hope this isn't too far off topic, as this is having a big impact on my testing.
I decided to run an A/B test on one of my GPSDOs: comparing the phase of the two 10MHz output channels. In the middle of the night, there was a long series of 35ns pops in the phase data. Strangely enough, there was nothing in the data collected directly from the unit involved. The preceding two days we had had a number of switching transients where the lights blinked but nothing shut down. So, putting one and one together, I suspect that a fair percentage of the strange results I've been getting has been power-grid related.
So, what to do? I've been looking at UPS devices, and I don't even understand enough to waste my money on a bad one. The two big questions seem to be "on-line" and "sine wave". Make that three: can I trust the mfgs claims? Is there something affordable that could run a pair of 5370s and maybe another 50W worth of DUTs for up to an hour or two and not be prey to power-line transients? Or would it be more cost effective to somehow monitor the power line for spikes or phase jumps and blow off tests or cut out the offending data? From time to time we get a thread on power-line nuts. Should I have been paying more attention?
GFS GPSDO list:
groups.yahoo.com/neo/groups/GFS-GPSDOs/info
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
--
If this email is spam, report it to
https://support.onlymyemail.com/view/report_spam/ODExMjI6MTg5OTEwNzgwNDpyb2JAbmMwYi5jb206ZGVsaXZlcmVk
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
if yo limit the Q you limit the effect also... by the way the Q is
already limited by the ohmic resistance of your transformer coils.
73
KJ6UHN
Alex
On 7/8/2016 10:08 PM, David wrote:
And I will add a high voltage power resistor to limit the Q.
On Fri, 8 Jul 2016 22:12:53 -0400, you wrote:
Hi
If you try this, be very careful with the voltage at the junction of the L and the C.
Bob
On Jul 8, 2016, at 9:52 PM, David davidwhess@gmail.com wrote:
I wonder how well a pair of high voltage transformers wired back to
back with a 60 Hz series resonate LC circuit between them would work
for removing power line glitches. They wouldn't do anything for
voltage regulation unlike a constant voltage transformer though. Time
to break out a couple of plate transformers and try it I guess.
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2016.0.7640 / Virus Database: 4613/12583 - Release Date: 07/08/16
Hi Bob:
The Sola 500 VA transformer is specified to hole up the line voltage for 3 ms. (but not a half cycle of the line
frequency).
I've connected the Sola CVS transformer to the output of the APC RS1500 backup UPS. (needed to replace the 2 batteries
in the main unit and probably within a year the 4 batteries in the optional battery pack.
http://www.prc68.com/I/Sola_CVS.html
http://www.prc68.com/I/PC.shtml#Backup_UPS
The Sola transformer is connected to the output of the RS1500. This will clean up any spikes or narrow drop outs on the
AC line since when the AC line is active the UPS does nothing.
My hope was that the transformer would clean up the modified square wave output of the UPS, but that does not happen.
Video of APC self test showing waveform on scope:https://youtu.be/DLE0mzAt7KY https://youtu.be/DLE0mzAt7KY
I think the modified square wave killed my HP 6200 flat bed scanner. The best scanner I've used and no longer made.
--
Have Fun,
Brooke Clarke
http://www.PRC68.com
http://www.end2partygovernment.com/2012Issues.html
The lesser of evils is still evil.
-------- Original Message --------
I hope this isn't too far off topic, as this is having a big impact on my testing.
I decided to run an A/B test on one of my GPSDOs: comparing the phase of the two 10MHz output channels. In the middle of the night, there was a long series of 35ns pops in the phase data. Strangely enough, there was nothing in the data collected directly from the unit involved. The preceding two days we had had a number of switching transients where the lights blinked but nothing shut down. So, putting one and one together, I suspect that a fair percentage of the strange results I've been getting has been power-grid related.
So, what to do? I've been looking at UPS devices, and I don't even understand enough to waste my money on a bad one. The two big questions seem to be "on-line" and "sine wave". Make that three: can I trust the mfgs claims? Is there something affordable that could run a pair of 5370s and maybe another 50W worth of DUTs for up to an hour or two and not be prey to power-line transients? Or would it be more cost effective to somehow monitor the power line for spikes or phase jumps and blow off tests or cut out the offending data? From time to time we get a thread on power-line nuts. Should I have been paying more attention?
GFS GPSDO list:
groups.yahoo.com/neo/groups/GFS-GPSDOs/info
time-nuts mailing list -- time-nuts@febo.com