HI
I would take a look at the “stuff” they make for wine cellars. It’s an application aimed
at the same sort of area size and done in much higher volume than an electronics
closet.
Bob
On Oct 26, 2016, at 1:58 PM, John Ackermann N8UR jra@febo.com wrote:
On 10/26/2016 1:00 PM, Richard (Rick) Karlquist wrote:
On 10/26/2016 8:59 AM, John Ackermann N8UR wrote:
I may have the opportunity to build a small "clock room" and am
considering whether I could make it an environmentally controlled space.
I'd like to learn about the options for doing this.
The space would probably be 6x8 feet or so, in a basement with one
outside wall.
I'm lost with the basic concept here. Help me understand this.
This room would be a large closet in my basement where two racks of various OCXO, Rb, Cs live. There wouldn't be a lot of in-and-out traffic. I'm not looking for 0.01 degree regulation -- <1 degree C and a few percent humidity throughout the year seems a reasonable goal.
What I envisioned was a very small heat pump or other heating/air-con unit coupled with some sort of proportional control. I just don't know where to start looking for that, or what other issues to be thinking about.
(I know the way time-nuts think, and I recall the great ideas posted here in the past about using an old refrigerator, or burying standards in a deep hole -- but this would be wrapped into a bigger construction project that I'm going to be managing from a distance, so I need to keep it fairly straight-forward.)
Thanks, all!
John
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
HI
I would take a look at the “stuff” they make for wine cellars. It’s an application aimed
at the same sort of area size and done in much higher volume than an electronics
closet.
Bob
> On Oct 26, 2016, at 1:58 PM, John Ackermann N8UR <jra@febo.com> wrote:
>
> On 10/26/2016 1:00 PM, Richard (Rick) Karlquist wrote:
>> On 10/26/2016 8:59 AM, John Ackermann N8UR wrote:
>>> I may have the opportunity to build a small "clock room" and am
>>> considering whether I could make it an environmentally controlled space.
>>> I'd like to learn about the options for doing this.
>>>
>>> The space would probably be 6x8 feet or so, in a basement with one
>>> outside wall.
>>
>> I'm lost with the basic concept here. Help me understand this.
>
> This room would be a large closet in my basement where two racks of various OCXO, Rb, Cs live. There wouldn't be a lot of in-and-out traffic. I'm not looking for 0.01 degree regulation -- <1 degree C and a few percent humidity throughout the year seems a reasonable goal.
>
> What I envisioned was a very small heat pump or other heating/air-con unit coupled with some sort of proportional control. I just don't know where to start looking for that, or what other issues to be thinking about.
>
> (I know the way time-nuts think, and I recall the great ideas posted here in the past about using an old refrigerator, or burying standards in a deep hole -- but this would be wrapped into a bigger construction project that I'm going to be managing from a distance, so I need to keep it fairly straight-forward.)
>
> Thanks, all!
>
> John
> ----
> _______________________________________________
> time-nuts mailing list -- time-nuts@febo.com
> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
> and follow the instructions there.
PK
Poul-Henning Kamp
Thu, Oct 27, 2016 7:25 AM
I may have the opportunity to build a small "clock room" and am
considering whether I could make it an environmentally controlled space.
I'd like to learn about the options for doing this.
You first need to decide what kind of clock room you want:
At one extreme you have a clock vault you never change anything in,
with incredibly stable temperature & humidity, but stabilization
times of days or weeks.
At the other end you have an environmental chamber which hits temperature
and humidity in a matter of minutes after you closed them.
If you want to do this low budget, consider getting a couple of old
fridges or freezers and run water of your chosen temperature
through their cooling loops. That way you can have multiple different
climates and keep soom stuff stable while you play with other stuff.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
--------
In message <5810D2D2.2070902@febo.com>, John Ackermann N8UR writes:
>I may have the opportunity to build a small "clock room" and am
>considering whether I could make it an environmentally controlled space.
> I'd like to learn about the options for doing this.
You first need to decide what kind of clock room you want:
At one extreme you have a clock vault you never change anything in,
with incredibly stable temperature & humidity, but stabilization
times of days or weeks.
At the other end you have an environmental chamber which hits temperature
and humidity in a matter of minutes after you closed them.
If you want to do this low budget, consider getting a couple of old
fridges or freezers and run water of your chosen temperature
through their cooling loops. That way you can have multiple different
climates and keep soom stuff stable while you play with other stuff.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Thu, Oct 27, 2016 7:31 AM
Rick, professional environmental chambers [...]
And they come up on fleabay with surprising regularity.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
--------
In message <CANy2iXrmyy2E9PBdgcqiUZgne_8rPL4KKuW2J4pDJLbJ+j1gXQ@mail.gmail.com>
, "William H. Fite" writes:
>Rick, professional environmental chambers [...]
And they come up on fleabay with surprising regularity.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
PK
Poul-Henning Kamp
Thu, Oct 27, 2016 7:41 AM
Probably the easiest is to get some glass/mineral wool insulation and
put it over all the walls, including ceiling and floor. I do not recommend
any foam or styropor based insulation as almost all of them are inflamable.
This should get you into the area of 10-100W/K thermal resistance for your
closet (assuming something like 4cm thick insulation gets about 40W/K).
Stop!
Over insulating is a 100% sure-fire way to get unstable temperature inside,
because it amplifies the consequences of any change in power dissipation.
It is a classic mistake to build a 100mm insulated enclosure inside an
office-like enviroment and end up having less stable temperature on
the inside than the outside.
Cinderblocks is a much better material for that scenario, because they
have both thermal mass and inertia (= heat capacity and heat impedance)
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
--------
In message <20161026210517.26c0fd397b1cae5ba9c12def@kinali.ch>, Attila Kinali w
rites:
>Probably the easiest is to get some glass/mineral wool insulation and
>put it over all the walls, including ceiling and floor. I do not recommend
>any foam or styropor based insulation as almost all of them are inflamable.
>This should get you into the area of 10-100W/K thermal resistance for your
>closet (assuming something like 4cm thick insulation gets about 40W/K).
Stop!
Over insulating is a 100% sure-fire way to get unstable temperature inside,
because it amplifies the consequences of any change in power dissipation.
It is a classic mistake to build a 100mm insulated enclosure inside an
office-like enviroment and end up having less stable temperature on
the inside than the outside.
Cinderblocks is a much better material for that scenario, because they
have both thermal mass and inertia (= heat capacity and heat impedance)
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
DJ
David J Taylor
Thu, Oct 27, 2016 9:17 AM
From: jimlux
You can buy the smallest "window" airconditioner and "plumb" it to your
chamber (I used dryer vent hose, cardboard, and lots of duct tape)
Attached is a plot temperature and RH of an insulated box about 1.2
meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
bottles of liquid.
The temperature is fairly stable, but the RH varies wildly - basically,
when the AC unit kicks on, it sucks all the water out of the air in the
box, and then, when it turns off, the (damp) walls of the box rapidly
rehumidify the air.
Thanks for that, Jim, and for the graph.
Your graph suggests to me that using /any/ form of artificial control may
give worse short-term results than simply leaving an underground,
uninhabited room with outside walls just "as-is". The slow daily variations
may be far more tolerable than excursions due to heaters etc. being switched
on and off.
Cheers,
David
SatSignal Software - Quality software written to your requirements
Web: http://www.satsignal.eu
Email: david-taylor@blueyonder.co.uk
Twitter: @gm8arv
From: jimlux
You can buy the smallest "window" airconditioner and "plumb" it to your
chamber (I used dryer vent hose, cardboard, and lots of duct tape)
Attached is a plot temperature and RH of an insulated box about 1.2
meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
bottles of liquid.
The temperature is fairly stable, but the RH varies wildly - basically,
when the AC unit kicks on, it sucks all the water out of the air in the
box, and then, when it turns off, the (damp) walls of the box rapidly
rehumidify the air.
_______________________________________________
Thanks for that, Jim, and for the graph.
Your graph suggests to me that using /any/ form of artificial control may
give worse short-term results than simply leaving an underground,
uninhabited room with outside walls just "as-is". The slow daily variations
may be far more tolerable than excursions due to heaters etc. being switched
on and off.
Cheers,
David
--
SatSignal Software - Quality software written to your requirements
Web: http://www.satsignal.eu
Email: david-taylor@blueyonder.co.uk
Twitter: @gm8arv
NM
Neville Michie
Thu, Oct 27, 2016 9:43 AM
The nature of air is that when you heat it by one degree Celcius the humidity falls by 10%.
That does not change the moisture content of the air, just the activity of the same amount of
water vapour with regards to any material with an equilibrium moisture content.
So it is important to control temperature fluctuation if you are going to control relative humidity.
cheers,
Neville Michie
On 27 Oct 2016, at 8:17 PM, David J Taylor david-taylor@blueyonder.co.uk wrote:
From: jimlux
You can buy the smallest "window" airconditioner and "plumb" it to your
chamber (I used dryer vent hose, cardboard, and lots of duct tape)
Attached is a plot temperature and RH of an insulated box about 1.2
meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
bottles of liquid.
The temperature is fairly stable, but the RH varies wildly - basically,
when the AC unit kicks on, it sucks all the water out of the air in the
box, and then, when it turns off, the (damp) walls of the box rapidly
rehumidify the air.
Thanks for that, Jim, and for the graph.
Your graph suggests to me that using /any/ form of artificial control may give worse short-term results than simply leaving an underground, uninhabited room with outside walls just "as-is". The slow daily variations may be far more tolerable than excursions due to heaters etc. being switched on and off.
Cheers,
David
SatSignal Software - Quality software written to your requirements
Web: http://www.satsignal.eu
Email: david-taylor@blueyonder.co.uk
Twitter: @gm8arv
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
The nature of air is that when you heat it by one degree Celcius the humidity falls by 10%.
That does not change the moisture content of the air, just the activity of the same amount of
water vapour with regards to any material with an equilibrium moisture content.
So it is important to control temperature fluctuation if you are going to control relative humidity.
cheers,
Neville Michie
> On 27 Oct 2016, at 8:17 PM, David J Taylor <david-taylor@blueyonder.co.uk> wrote:
>
> From: jimlux
>
> You can buy the smallest "window" airconditioner and "plumb" it to your
> chamber (I used dryer vent hose, cardboard, and lots of duct tape)
>
> Attached is a plot temperature and RH of an insulated box about 1.2
> meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
> bottles of liquid.
>
> The temperature is fairly stable, but the RH varies wildly - basically,
> when the AC unit kicks on, it sucks all the water out of the air in the
> box, and then, when it turns off, the (damp) walls of the box rapidly
> rehumidify the air.
> _______________________________________________
>
> Thanks for that, Jim, and for the graph.
>
> Your graph suggests to me that using /any/ form of artificial control may give worse short-term results than simply leaving an underground, uninhabited room with outside walls just "as-is". The slow daily variations may be far more tolerable than excursions due to heaters etc. being switched on and off.
>
> Cheers,
> David
> --
> SatSignal Software - Quality software written to your requirements
> Web: http://www.satsignal.eu
> Email: david-taylor@blueyonder.co.uk
> Twitter: @gm8arv
> _______________________________________________
> time-nuts mailing list -- time-nuts@febo.com
> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
> and follow the instructions there.
AK
Attila Kinali
Thu, Oct 27, 2016 11:12 AM
Hoi Poul-Henning,
On Thu, 27 Oct 2016 07:41:48 +0000
"Poul-Henning Kamp" phk@phk.freebsd.dk wrote:
Probably the easiest is to get some glass/mineral wool insulation and
put it over all the walls, including ceiling and floor. I do not recommend
any foam or styropor based insulation as almost all of them are inflamable.
This should get you into the area of 10-100W/K thermal resistance for your
closet (assuming something like 4cm thick insulation gets about 40W/K).
Stop!
Over insulating is a 100% sure-fire way to get unstable temperature inside,
because it amplifies the consequences of any change in power dissipation.
It is a classic mistake to build a 100mm insulated enclosure inside an
office-like enviroment and end up having less stable temperature on
the inside than the outside.
No! Don't Stop! :-)
That's why the next section I wrote described how to get rid of the
excess heat in a controlled fashio. Of course, simply just insulating
the room without giving it a lot of thermal mass or any form of control
of the heat production/exchange will not stabilize the room.
Attila Kinali
--
It is upon moral qualities that a society is ultimately founded. All
the prosperity and technological sophistication in the world is of no
use without that foundation.
-- Miss Matheson, The Diamond Age, Neil Stephenson
Hoi Poul-Henning,
On Thu, 27 Oct 2016 07:41:48 +0000
"Poul-Henning Kamp" <phk@phk.freebsd.dk> wrote:
> >Probably the easiest is to get some glass/mineral wool insulation and
> >put it over all the walls, including ceiling and floor. I do not recommend
> >any foam or styropor based insulation as almost all of them are inflamable.
> >This should get you into the area of 10-100W/K thermal resistance for your
> >closet (assuming something like 4cm thick insulation gets about 40W/K).
>
> Stop!
>
> Over insulating is a 100% sure-fire way to get unstable temperature inside,
> because it amplifies the consequences of any change in power dissipation.
>
> It is a classic mistake to build a 100mm insulated enclosure inside an
> office-like enviroment and end up having less stable temperature on
> the inside than the outside.
No! Don't Stop! :-)
That's why the next section I wrote described how to get rid of the
excess heat in a controlled fashio. Of course, simply just insulating
the room without giving it a lot of thermal mass or any form of control
of the heat production/exchange will not stabilize the room.
Attila Kinali
--
It is upon moral qualities that a society is ultimately founded. All
the prosperity and technological sophistication in the world is of no
use without that foundation.
-- Miss Matheson, The Diamond Age, Neil Stephenson
J
jimlux
Thu, Oct 27, 2016 1:06 PM
On 10/27/16 2:17 AM, David J Taylor wrote:
From: jimlux
You can buy the smallest "window" airconditioner and "plumb" it to your
chamber (I used dryer vent hose, cardboard, and lots of duct tape)
Attached is a plot temperature and RH of an insulated box about 1.2
meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
bottles of liquid.
The temperature is fairly stable, but the RH varies wildly - basically,
when the AC unit kicks on, it sucks all the water out of the air in the
box, and then, when it turns off, the (damp) walls of the box rapidly
rehumidify the air.
Thanks for that, Jim, and for the graph.
Your graph suggests to me that using /any/ form of artificial control
may give worse short-term results than simply leaving an underground,
uninhabited room with outside walls just "as-is". The slow daily
variations may be far more tolerable than excursions due to heaters etc.
being switched on and off.
Indeed.. a large mass varies slowly.
(hence the suggestions in previous years for finding caves, digging a
mine shaft, etc)
On 10/27/16 2:17 AM, David J Taylor wrote:
> From: jimlux
>
> You can buy the smallest "window" airconditioner and "plumb" it to your
> chamber (I used dryer vent hose, cardboard, and lots of duct tape)
>
> Attached is a plot temperature and RH of an insulated box about 1.2
> meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
> bottles of liquid.
>
> The temperature is fairly stable, but the RH varies wildly - basically,
> when the AC unit kicks on, it sucks all the water out of the air in the
> box, and then, when it turns off, the (damp) walls of the box rapidly
> rehumidify the air.
> _______________________________________________
>
> Thanks for that, Jim, and for the graph.
>
> Your graph suggests to me that using /any/ form of artificial control
> may give worse short-term results than simply leaving an underground,
> uninhabited room with outside walls just "as-is". The slow daily
> variations may be far more tolerable than excursions due to heaters etc.
> being switched on and off.
>
Indeed.. a large mass varies slowly.
(hence the suggestions in previous years for finding caves, digging a
mine shaft, etc)
J
jimlux
Thu, Oct 27, 2016 1:12 PM
On 10/27/16 2:43 AM, Neville Michie wrote:
The nature of air is that when you heat it by one degree Celcius the humidity falls by 10%.
That does not change the moisture content of the air, just the activity of the same amount of
water vapour with regards to any material with an equilibrium moisture content.
So it is important to control temperature fluctuation if you are going to control relative humidity.
cheers,
In this particular case, I did do the calculation of "mass fraction of
water" from the data - the AC really does pull the water out of the air.
The "test article" in this case has relatively small air volume, and a
large surface area of wood. Water goes out fast, comes in slow.
There might also be a surface condensation issue on the glass surfaces.
If you look at the wet bulb temperature, it runs a few degrees below the
air temperature, except when the AC is on, when it plunges several
degrees in seconds.
On 27 Oct 2016, at 8:17 PM, David J Taylor david-taylor@blueyonder.co.uk wrote:
From: jimlux
You can buy the smallest "window" airconditioner and "plumb" it to your
chamber (I used dryer vent hose, cardboard, and lots of duct tape)
Attached is a plot temperature and RH of an insulated box about 1.2
meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
bottles of liquid.
The temperature is fairly stable, but the RH varies wildly - basically,
when the AC unit kicks on, it sucks all the water out of the air in the
box, and then, when it turns off, the (damp) walls of the box rapidly
rehumidify the air.
Thanks for that, Jim, and for the graph.
Your graph suggests to me that using /any/ form of artificial control may give worse short-term results than simply leaving an underground, uninhabited room with outside walls just "as-is". The slow daily variations may be far more tolerable than excursions due to heaters etc. being switched on and off.
Cheers,
David
SatSignal Software - Quality software written to your requirements
Web: http://www.satsignal.eu
Email: david-taylor@blueyonder.co.uk
Twitter: @gm8arv
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.
On 10/27/16 2:43 AM, Neville Michie wrote:
> The nature of air is that when you heat it by one degree Celcius the humidity falls by 10%.
> That does not change the moisture content of the air, just the activity of the same amount of
> water vapour with regards to any material with an equilibrium moisture content.
> So it is important to control temperature fluctuation if you are going to control relative humidity.
> cheers,
In this particular case, I did do the calculation of "mass fraction of
water" from the data - the AC really does pull the water out of the air.
The "test article" in this case has relatively small air volume, and a
large surface area of wood. Water goes out fast, comes in slow.
There might also be a surface condensation issue on the glass surfaces.
If you look at the wet bulb temperature, it runs a few degrees below the
air temperature, except when the AC is on, when it plunges several
degrees in seconds.
> Neville Michie
>
>
>> On 27 Oct 2016, at 8:17 PM, David J Taylor <david-taylor@blueyonder.co.uk> wrote:
>>
>> From: jimlux
>>
>> You can buy the smallest "window" airconditioner and "plumb" it to your
>> chamber (I used dryer vent hose, cardboard, and lots of duct tape)
>>
>> Attached is a plot temperature and RH of an insulated box about 1.2
>> meter wide, 2 meters tall and 60 cm deep, filled with 100 or so 750 ml
>> bottles of liquid.
>>
>> The temperature is fairly stable, but the RH varies wildly - basically,
>> when the AC unit kicks on, it sucks all the water out of the air in the
>> box, and then, when it turns off, the (damp) walls of the box rapidly
>> rehumidify the air.
>> _______________________________________________
>>
>> Thanks for that, Jim, and for the graph.
>>
>> Your graph suggests to me that using /any/ form of artificial control may give worse short-term results than simply leaving an underground, uninhabited room with outside walls just "as-is". The slow daily variations may be far more tolerable than excursions due to heaters etc. being switched on and off.
>>
>> Cheers,
>> David
>> --
>> SatSignal Software - Quality software written to your requirements
>> Web: http://www.satsignal.eu
>> Email: david-taylor@blueyonder.co.uk
>> Twitter: @gm8arv
>> _______________________________________________
>> time-nuts mailing list -- time-nuts@febo.com
>> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
>> and follow the instructions there.
>
> _______________________________________________
> time-nuts mailing list -- time-nuts@febo.com
> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
> and follow the instructions there.
>
PK
Poul-Henning Kamp
Thu, Oct 27, 2016 1:28 PM
Stop!
Over insulating is a 100% sure-fire way to get unstable temperature inside,
because it amplifies the consequences of any change in power dissipation.
It is a classic mistake to build a 100mm insulated enclosure inside an
office-like enviroment and end up having less stable temperature on
the inside than the outside.
No! Don't Stop! :-)
That's why the next section I wrote described how to get rid of the
excess heat in a controlled fashio. Of course, simply just insulating
the room without giving it a lot of thermal mass or any form of control
of the heat production/exchange will not stabilize the room.
Attila, I did read that.
You are right in a certain set of circumstances, for instance in a
already climate-regulated office space.
But your model is a recipe for grief and disaster if you do it in
a typical basement, on about 2/3 of the inhabited area of the planet
where you cannot ignore the humidity.
In general in a basement, it is a better idea to set up a closed
space and manage the humidity inside it, than it is to move the
humidity in and out of it.
WRT to humidity, that's a very unlinear relationship, but you can
get far by remembering these five rules:
-
Warm air holds more absolute humidity (ie: g/m³) than colder air.
-
At the same temperture, wetter air is lighter than dryer air.
-
The temperature is never the same.
-
Condensation should be avoided, period.
-
You cannot "feel" absolute humidity, always measure it.
And yes, go ahead and look up number two, it's true. Dehumidifiers
belong on shelves under the ceiling, not on the floor.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.
--------
In message <20161027131226.0d5a72e62b2c91f2e13b637e@kinali.ch>, Attila Kinali w
rites:
>> Stop!
>>
>> Over insulating is a 100% sure-fire way to get unstable temperature inside,
>> because it amplifies the consequences of any change in power dissipation.
>>
>> It is a classic mistake to build a 100mm insulated enclosure inside an
>> office-like enviroment and end up having less stable temperature on
>> the inside than the outside.
>
>No! Don't Stop! :-)
>
>That's why the next section I wrote described how to get rid of the
>excess heat in a controlled fashio. Of course, simply just insulating
>the room without giving it a lot of thermal mass or any form of control
>of the heat production/exchange will not stabilize the room.
Attila, I did read that.
You are right in a certain set of circumstances, for instance in a
already climate-regulated office space.
But your model is a recipe for grief and disaster if you do it in
a typical basement, on about 2/3 of the inhabited area of the planet
where you cannot ignore the humidity.
In general in a basement, it is a better idea to set up a closed
space and manage the humidity inside it, than it is to move the
humidity in and out of it.
WRT to humidity, that's a very unlinear relationship, but you can
get far by remembering these five rules:
* Warm air holds more *absolute* humidity (ie: g/m³) than colder air.
* At the same temperture, wetter air is lighter than dryer air.
* The temperature is never the same.
* Condensation should be avoided, period.
* You cannot "feel" absolute humidity, always measure it.
And yes, go ahead and look up number two, it's true. Dehumidifiers
belong on shelves under the ceiling, not on the floor.
--
Poul-Henning Kamp | UNIX since Zilog Zeus 3.20
phk@FreeBSD.ORG | TCP/IP since RFC 956
FreeBSD committer | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.